I am wondering if anyone is running a RIMS setup with a 30 amp control panel. I am looking into this option but I am unsure of how to wire the RIMS as I will be running 1375w (11.5 amps) for the RIMS and if I were to run the BK or HLT at the same time (5500w/~23 amp) I will be tripping breakers.
Should I just be considering a HERMS for this reason alone? I won't be building my control panel for a while as I plan to run my BK and HLT on PWM (already setup for 40amp) for a while and was going to use a PID I have wired up for my smoker to run the RIMS in the meantime.