Since relay1 is rated at 5A, will a fuse be needed along that path, e.g. before the e-stop?
If so, what about the path that connects L2 to the other set of the relay1 contacts as well?
And if that one requires a fuse too, could you connect both sets of relay1 contacts to the same incoming L2 (i.e. the path after the e-stop) and then only 1 fuse would be needed?
I think you're confused.
R1 never touches L2. the coil goes between L1 and Neutral.
Here is how the circuit works.
The e-stop is normally closed, so it is passing current to the start button and R1 contant.
The run button is momentary, so after you lift your finger the circuit opens again.
When you press the run button it completes the circuit to the coil of R1
R1 closes it's contacts, one of which energizes C1 allowing current to pass down L1 and L2 to the rest of the devices.
The second contact of R1 closes bypassing the momentary start button. So when you left your finger and the contacts open R1 will keep it self energized.
When you press the E-Stop it break the circuit going to R1's coil, in turn breaking C1's coil, which ultimately disconnects power from the rest of the brewery.
To start the system again the E-stop needs to be reset and the start button pressed again.
As far as fusing goes, The wire going to the coil needs to be protected from running an over current.
When you get to devices like relays, you don't have to use a fuse for each individual one, you can fuse a terminal bus to the rating of the wire used for the relays. So if it is 14Awg, you would put a 15 amp fuse on it. After that fuse you can use 14Awg wire to control up to as many relays 15amps will support. Say the coil draws .1 Amps to energize, you could use that 15 Amp bus to power 15A/.1A*.50 Relays (that would be 150 relays derated by 50% to avoid nuisance pops, 75 relays)
Same goes for the contactors.
Does this help or have I muddied the waters?