Say PassedPawn, i'm trying to understand something here..
I am looking at the toggle switch you got from digikey, and looking at the specs it says it's rated 25A-125V
How is that able to work for us then, if we run about 23A with a 5500W at 240V element?

Reason i am asking, at the hardware store they have 25A-125W toggles for about 6 bucks or so.. I just wanna make sure they'll work.


edit:
Really what i am looking for is a switch to only switch one leg of the 240V, i would be open for any other suggestions ;) I am not going to switch the thermocouple cable, just unplug/plug different one in.
 
That switch only has the low-voltage low-current control signals to the SSRs. The SSRs do the heavy lifting here.

In other words, I'm just routing the control signal from the PID to whichever relay (SSR) I want to be on. The switch also routes the correct thermocouple signal back to the PID.
 
It helps to consider the water analogy again:

voltage (volts) = pressure, (psi)
current (amps) = flow (gpm)
resistance (?) = resistance (ohms)


I.e., I = 5500W / 240VAC = 23A.​

I liked the water analogy. Would it give a better picture by stating it this way?


voltage (volts) = pressure, (psi)
current (amps) = flow (gpm)
resistance (ohms) = resistance (pipe diameter)
 
Hey Passedpawn, I'm trying to put together something similiar for a friend. He has 4 5500W elements all on their own 240V-30A breakers. Planning on putting 1 PID to control all 4. Will we need 4 or 2 D2425D SSR's to handle the load. I like the idea of having both legs being controlled. Is the D2425D rated for 25AX2? Also a single SSR has 4 connections, Does the dual have 6? Having trouble understanding the Dual SSR. Thanks
 
Does anyone know if an electric system can be done safely on a 3 prong system? We have an old 1950's house and they only have 3 prong 240v outlets. If I have an electrician install a GFCI breaker in our panel would this provide the protection I need?
 
Does anyone know if an electric system can be done safely on a 3 prong system? We have an old 1950's house and they only have 3 prong 240v outlets. If I have an electrician install a GFCI breaker in our panel would this provide the protection I need?

It will work fine in a 3-prong 240VAC outlet. There are some instances where it might not be as safe as a 4-prong (Line-Line-Neutral-GND). I would strongly suggest that the electrician change the outlet to add the safety ground. Shouldn't be a big deal do do that if he can pull a ground from nearby wire.
 
Hey Passedpawn, I'm trying to put together something similiar for a friend. He has 4 5500W elements all on their own 240V-30A breakers. Planning on putting 1 PID to control all 4. Will we need 4 or 2 D2425D SSR's to handle the load. I like the idea of having both legs being controlled. Is the D2425D rated for 25AX2? Also a single SSR has 4 connections, Does the dual have 6? Having trouble understanding the Dual SSR. Thanks

The pinout of the dual SSR is just 2 of everything, like this:

D2425D_Pinout.png
D2425D_mechs.png


Some of the duals have screw terminals for the outputs, others (like mine) have Faston lugs. They all work fine in our application. The control side has pins on 0.1" spacing for standard connectors, or you can solder to them or connect to them in a bunch of ways, or some models also have lugs for the control signals.

Here's the derating curve. This is Combined Output Current, so it is the sum of the current on both channels. With a poor heat sink (the chinese varieties) The heat conduction is poor (i.e., 5°C/W) and you won't get to run the SSR very hard. With a good heat sink (mine is 0.7°C/W) you can run it full tilt. I use a 5500W element, and it goes through this dual, so both channels are geting about 23A, for a total of 46A. You can see that at an ambient temp of 20°C, I'd need a heat sink of 1.0°C/W or better. I got one. You can see my heat sink somewhere earlier in this thread (I think).

D2425D_Derating_curves.png
 
Got it. Great explanation. So to run 4 5500W elements on 1 PID: Jumper the inputs to 4 25A- DSSR's. Will we need 2 of the heatsinks you posted?
 
Got it. Great explanation. So to run 4 5500W elements on 1 PID: Jumper the inputs to 4 25A- DSSR's. Will we need 2 of the heatsinks you posted?

Yes.

and maybe (if you are driving all the DSSRs at the same time). My heatsink carries two SSRs (or DSSRs). It (the heat sink) is properly spec'ed for one of those DSSRs going full tilt, but not both at the same time - that would be double the heat dissipation needed from the heat sink. You could probably do it with a fan over the heat sink, but with just passive cooling on the heat sink I think it's not gonna keep the SSRs cool enough.
 