So out of range on the heat transfer capacity section means the exchanger is too small to meet the given the conditions.
100% heat transfer capacity means it will take all available heat transfer area to meet requirements.
We like to see heat transfer capacity in the 80th percentile.
So, given your requirements, you are asking for your hot fluid to enter the exchanger at 220 and leave the exchanger at 70.
Your conditions with 6 pgm hot and 20 gpm cold will transfer 486703.96 BTUs.
Now, we can also adjust flow rates, lets say we reduce flow rate on the hot side to get our required temperature drop:
http://www.carlsonhx.com/index.php?...h=1&sgh=1.080&tci=65&tco=&gpmc=20&shc=1&sgc=1
A 20.0 will handle this load, but we'll only be transferring 121675.99 BTUs
Let's look at it from another angle:
Looking at our online Volume calculator:
http://www.carlsonhx.com/index.php?item=calc&view=vol
Specific Gravity 1.08, Delta T 150, Gals 220 (assuming 220 gallon tank) requires 297430 BTU
So it will take the 297430 BTU to cool the 220 gallons in an hour.
(BTU being the amount of heat required to raise 1 gallon of water 1 degree in one hour).
Let adjust our requirements:
http://www.carlsonhx.com/index.php?...h=1&sgh=1.080&tci=65&tco=&gpmc=20&shc=1&sgc=1
A 20.0 will handle this. Now, we're not getting 70 degrees directly out of the exchanger, but we are cooling the tank in an hour.
Additionally, if we increase the hot flow rate to even just 10 gpm instead of 6, we can get by with a smaller exchanger:
http://www.carlsonhx.com/index.php?...h=1&sgh=1.080&tci=65&tco=&gpmc=20&shc=1&sgc=1
This is a fully welded industrial unit built to last. Made of entirely food grade 316L Stainless, the unit itself will not be susceptible to biological attack or galvanic corrosion as other units where dissimilar metals are used. It will work well in a brew environment. We can also make modifications such as custom fittings and brackets to the product as well.