I am a union carpenter and what your talking about doing is not a big deal.
Palm Springs
just guessing on pics here... so don't take this too serious and run out to buy something. But this might help when you are talking to a local on doing some work... don't let them run ya round for big $$
loading on top chord (dead load) =
Asphalt 4psf (over calc for 2 layers)
15lb felt .15spf
1/2 OSB (most likely) 1.43psf
Blown insl. .1psf
possible 2x6 chords 1.5psf
added 3psf for wood shingles over asphalt
misc mech. 1.5psf
1" plaster ceiling (another guess) 8psf
20psf standard top chord live load
10psf standard bottom chord
total loading: 49.68, lets say 50psf (guess)
Now, looks like a 20' span (another guess)... so 50psf x 20span = 1,000
1,000plf would be each truss' (or rafter's) load bearing at the walls, 2 bearing walls... one at each end & we break that down to 500# each bearing but @ 1' (because we dealt with per sq ft earlier)... they look to be 2' o.c. (on center spacing) - so 500plf x 2 to cover the 2' spacing... & we're back to 1,000# bearing load at each end of the truss/rafters
if a beam is taking 1,000# every 2' we can say it has 500# every 1' of length.
If the opening will need a 10' beam, then 10 x 500 = 5,000# of load from the beam. since it bears on 2 posts (or will be...) each post will see 2,500# of load from each end of the bm.
a 3 1/2" x 9.5" glulam bm should work, as will a 3-ply 1 3/4" x 7.25" Microllam LVL
A lot of ifs and buts though... this is why it might be best to have an engineer come look & do a jobsite check. Better to know for sure than guess. A bowed ceiling and cracking plaster later on would suck and cost an eff'n ton more.
One contractor came out took a look and said 4x4 posts and 4x8 header...if he could fit it, 4x6if he couldnt. I have a truss company like a block away, do most sell to the public? Im working long days so im gone 6 to 6 and its hard to get over there. And i believe the studs are 16 on center. Not sure how much more that changes thigs. I will get a good measurement of the span when i get home today
I hate to put it this way, but a lot of that 'depends on the loading' of your counter.
However if you have L brackets like the picture that are about the full dept of the overhang, 4 of them on a 4 foot wall should be sufficent. I might get some smaller ones and put them on the other side to improve rigidity. - but then I'm from the 'when in doubt over build' school
Cut it. Go to the next full joist in either direction of the opening and double it up (either side of the joist, whichever is convenient). Cut the joist out and then box it in with 2 more members per side. Here's how it should look. You may have more than one cut joist in the opening, I only drew one.
Grey - Walls
Green - Existing joists
Red - New framing
Blue - Optional blocking to make the opening the size you want. May need to double up if trimming the hole with moulding wider than 1.5"
The rof slopes down right there but there is room to crawl up and opens wide once your upIn the photo, it looks like the rafter above the fan does not leave much headroom. Do you know if there is enough headroom there to meet your fire code?
So the existing joist only need to be doubled up the width of the hallway correct?, not he full length of the joist?