2 gauges seems a bit large for brewery use. On the upside, now you use your arc welder in the neighbor's yard when helping him fix his trailer.
Lol.
But doesn’t everyone say bigger is better?
Once i measure it out I may or may not keep some of it and trade the rest or something?
I actually suspected this was the case but I have to ask, Is there anyone out there running 6awg power cord from their outlet to their 30a brew panels? I would suspect there's far more people using 10/4 cable for this situation. Especially with their panels typically drawing around 25-26 amps with an element and pump running. I do not have a nuetral on my 30amp panel or a need for one with dc pumps so I guess im ok either way.this is why i hate it when cable manufacturers publish ampacity values for their product. there are a multitude of installation conditions, environmental considerations, etc. that can modify the allowable ampacity of a cable. plus, code references can change with new nec editions. the southwire literature references nec table 400.5, which hasn't existed since the 2008 edition of the nec. yes, in 2011 it was changed to table 400.5(A)(1) and (2), a minor change but a change nonetheless.
anyway, the referenced table does indeed indicate a 25 amp limit on 10/4 seoow cable (column a in the table). but what is not addressed is the table footnotes which provide the basis for determining the allowable ampacity. the 25 amp limit (as opposed to 30 amp indicated in column b) is based on the assumption that three of the conductors in the cable are current carrying. if only two of the conductors are current carrying (i.e. two hots and no neutral for an element), then the cable falls into the column b ampacity values and the full 30 amp value can be used. now if this was a main power cord to a brew panel with 120v loads, then the cable would be limited to 25 amps, since three of the conductors are carrying current.
long story short, you can get the full 30 amps out of the 10/4 but as others have stated, it is big and bulky and probably not worth the hassle.
I actually suspected this was the case but I have to ask, Is there anyone out there running 6awg power cord from their outlet to their 30a brew panels? I would suspect there's far more people using 10/4 cable for this situation. Especially with their panels typically drawing around 25-26 amps with an element and pump running. I do not have a nuetral on my 30amp panel or a need for one with dc pumps so I guess im ok either way.
My favorite ampacity table has the following footnote: "A conductor that is used to carry an unbalanced current from the other conductors is not considered to be a current carrying conductor." [emphasis added] I read that as saying two hots plus neutral gets to use the higher, two current carrying conductor limit. This makes sense, since whatever current flows thru the neutral is not flowing in one of the hots. For example: for a 28A 240V load and a 2A 120V load, one of the hots will be carrying 30A, the other hot will only carry 28A, and the neutral will carry 2A. Thus 30A source current and 30A return current, same as if you had a single 30A 240V load. Three current carrying conductors would be the case for 3-phase power, where all conductors carry pretty much the same current.this is why i hate it when cable manufacturers publish ampacity values for their product. there are a multitude of installation conditions, environmental considerations, etc. that can modify the allowable ampacity of a cable. plus, code references can change with new nec editions. the southwire literature references nec table 400.5, which hasn't existed since the 2008 edition of the nec. yes, in 2011 it was changed to table 400.5(A)(1) and (2), a minor change but a change nonetheless.
anyway, the referenced table does indeed indicate a 25 amp limit on 10/4 seoow cable (column a in the table). but what is not addressed is the table footnotes which provide the basis for determining the allowable ampacity. the 25 amp limit (as opposed to 30 amp indicated in column b) is based on the assumption that three of the conductors in the cable are current carrying. if only two of the conductors are current carrying (i.e. two hots and no neutral for an element), then the cable falls into the column b ampacity values and the full 30 amp value can be used. now if this was a main power cord to a brew panel with 120v loads, then the cable would be limited to 25 amps, since three of the conductors are carrying current.
long story short, you can get the full 30 amps out of the 10/4 but as others have stated, it is big and bulky and probably not worth the hassle.
you know, i never really thought about that before but i suppose it could be a code violation to run #10 cord to a 30 amp panel with 240v and 120v loads. would need the load to be above 25 amps at any given time. with a 5500 watt element, a chugger pump and a few indicating lights, it gets reeeal close. practically, it is fine if over 25 amps but technically, a violation.
Yes exactly .. Thats when the actual amp rating of the cable is used otherwise we would just say 10awg is good for 24a right?So if not 3 hrs one could exceed 80%? Assuming wires and other components are rated correctly.
The idea is running the cable at 3hrs or more at 100% draw causes more heat and puts more strain on the insulation and connections if I understand it right.