I'm trying to figure out if I can brew again in my new house without going back outside and using a propane burner.
I'm a renter and I'm trying to keep modifications and costs down but would really love to keep brewing on my electric system.

It's a 30amp 240v Electric Brewing Supply panel with a 4 prong plug. I had a GFCI breaker at the old house and would do the same at the new house but I'm trying to figure out what my best(safe, not too expensive and not doing too much modification to the house) option is to work with the 3 prong dryer outlet I now have.

What can I do to use my existing panel with minimal work?
 
You'll need a 4 prong to 3 prong adapter.

These normally have a ground wire attached that you either plug into the ground of a nearby outlet or use an extension cord plugged into a nearby outlet and the ground wire from the adapter goes into the ground of the extension cord.

Here's an example, it will help to know the NEMA plug and receptacle types when searching (i.e. 10-30p to 14-30r, etc...)

https://www.amazon.com/M1A2-Adapter-Safety-Ground-10-30P/dp/B09P3HWK1F
 
What type of plug did you have and what type do you now have? See a reference like: https://www.bsaelectronics.com/pages/nema-plug-and-outlet-chart

The important factors are 1) the amps (ideally the amp rating of the circuit matches the amp rating of your controller/plug) and 2) if a neutral wire is needed to provide 120V. The plug will have two hot wires to provide 240V and should also have a ground wire. 120V is provided by using one of the hots and the neutral.

Your "3 prong dryer outlet" sounds like it might be the outdated NEMA 10-30. These outlets have two hots to give your 240V, a neutral wire to provide 120V, but they do not have a ground. I would note that there is a fine line between what could be classified as a "ground" and a "neutral" wire in these outlets. Since this is a dedicated circuit, the neutral wire runs directly back to your panel and connects to the same bar as other ground wires. But since your control panel has a 4 prong plug, you likely need BOTH a neutral and a ground. You would not be able to adapt this 3 prong outlet directly to your 4 prong plug.

Edit: I sounds like the controller uses a NEMA 14-30 based on this info https://shop.theelectricbrewery.com...s/standard-30a-electric-brewery-control-panel:

The Standard 30A Electric Brewery Control Panel is usually plugged into a wall outlet using our 30A control panel power cord which requires a standard North American dryer receptacle (4-prong 30A/240V). Ask your electrician to install a NEMA 14-30R receptacle. In the electrical breaker panel, the circuit breaker must be a 30A / 240V 2-pole breaker. We recommend that the breaker include GFCI protection.
 
Last edited:
I am looking into adding a ground to my 10-30r 3 prong by doing a short run to my water heater or AC handler. Much shorter than to the panel. Looking into the viability and safety of this right now. Maybe it could work for you.
 
Adapter with separate ground:

https://www.amazon.com/Electric-3-Prong-Receptacle-Connector-Compliant/dp/B08BL3NKGB

1000006622.jpg

Not sure of the legalities of this particular configuration. Also have to verify the plug like @CascadesBrewer suggested.
 
What type of plug did you have and what type do you now have? See a reference like: https://www.bsaelectronics.com/pages/nema-plug-and-outlet-chart

The important factors are 1) the amps (ideally the amp rating of the circuit matches the amp rating of your controller/plug) and 2) if a neutral wire is needed to provide 120V. The plug will have two hot wires to provide 240V and should also have a ground wire. 120V is provided by using one of the hots and the neutral.

Your "3 prong dryer outlet" sounds like it might be the outdated NEMA 10-30. These outlets have two hots to give your 240V, a neutral wire to provide 120V, but they do not have a ground. I would note that there is a fine line between what could be classified as a "ground" and a "neutral" wire in these outlets. Since this is a dedicated circuit, the neutral wire runs directly back to your panel and connects to the same bar as other ground wires. But since your control panel has a 4 prong plug, you likely need BOTH a neutral and a ground. You would not be able to adapt this 3 prong outlet directly to your 4 prong plug.

Edit: I sounds like the controller uses a NEMA 14-30 based on this info https://shop.theelectricbrewery.com...s/standard-30a-electric-brewery-control-panel:

The Standard 30A Electric Brewery Control Panel is usually plugged into a wall outlet using our 30A control panel power cord which requires a standard North American dryer receptacle (4-prong 30A/240V). Ask your electrician to install a NEMA 14-30R receptacle. In the electrical breaker panel, the circuit breaker must be a 30A / 240V 2-pole breaker. We recommend that the breaker include GFCI protection.
Dryer outlet is the old Nema 10-30 and my controller is using the newer Nema 14-30
 