If the indicator light was wired between SSR terminal 1 and the black hot line, the light would be on whenever the element power enable switch (Leviton 3032) was on. To get Mike's behavior, you have to wire the indicator between terminals 1 and 2 of the SSR.I have a couple ideas of what might have gone wrong. If you accidentally wired the indicator light to terminal 1 (power input) of the SSR as shown in Doug's schematic instead of terminal 2 (power output), the indicator would be on when the SSR is switched off, and possibly the load of the element dims the indicator, making it appear to be off. A more likely scenario is that the indicator is wired between terminals 1 and 2. In this case, the indicator would light when the element is plugged in and the SSR is off, and then the indicator shuts off when the SSR fires because the voltage difference between terminals 1 and 2 would be zero. An easy way to check this is to see if the indicator turns off when the SSR is off and the element is unplugged. Seems like a simple fix to me.
Brew on