however to be fair, the above reasoning does not take into full consideration art. 310.16 of the national electrical code. As the title of Art 310.16 states "Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts, 60°C Through 90°C (140°F Through 194°F), Not More Than Three Current-Carrying Conductors in Raceway, Cable, or Earth (Directly Buried), Based on Ambient Temperature of 30°C (86°F)", the part you are concerned with is the current-carrying wording. The ground is not considered current carrying therefore you do not need to derate 6/4 soow if one of the wires involved is to be used for grounding purposes.
posted in 2 parts to allow a more thorough thought process, therefore with more consideration of the n.e.c, 6/4 soow wiring is suitable to be used for a hot hot nuetral and ground at 55 amps