So we never really discussed why hot water heaters don't need gfci. Any ideas?
They are wired in series. The top one takes precedence because that is where the hot water comes out. Once the top thermostat is satisfied it provides power to the bottom. It turns on if needed. Once the top cools off, like you are in the shower, it takes control back and kicks on the top element.
So we never really discussed why hot water heaters don't need gfci. Any ideas?
First off, it is a cold water heater. If the water were already hot we would have no reason to heat it. "Water heater" works for me
I think it was said but a water heater is an appliance. It is tucked away in a utility room or basement and is rarely even touched. Metal water lines are the best source of ground in a house. They are a required electrode when available. A properly bonded/grounded water heater poses no risk because it IS "ground". It should be the point that your GFCI receptacles use as reference.
Metallic water lines are a good electrical ground because they are required by code to be bonded to the power company ground rod, usually at the meter, and not because they come by it naturally.
Were it not for being bonded back to the power utility ground rod, they might, or might not, be a good, reliable earth ground.
This bonding is done to prevent water lines from accidentally being energized if they were to make contact with an energized conductor anywhere in the home.
Having electrically energized plumbing fixtures is a definite health hazard, which is why they are required to be grounded.
PEX, PVC, or other plastic plumbing systems are treated differently.
Wait a minute, I thought we were talking about cold water heaters?![]()
My bad. I guess I was focused on the control path. I've been gas for the past 22 years.You got it right except the series part. The elements are wired parallel but controlled just as you described.
Yes, it technically could be used, however it would violate electrical code, and the ground clamps used for piping that size are extremely expensive. A ground clamp for 1/2" up to 1" pipe is about 5$. When you jump to 1 1/4" ground clamp the price jumps to about 50$ each.
Also, some meters like the Fluke T5-1000 only measure resistance up to the 1000 ohm range.
Relying only on a breaker and not a GFCI to protect you in case of a ground fault is plain stupid, and what we in the electrical trade would call natural selection. If there is an electrical fault to ground, the breaker may not trip (for a handful of reasons) and still create a shock hazard. Use the GFCI and don't disconnect the ground. By tripping, it is doing it's job.
You said their is a ground lug on the GFCI... What brand/model is it? I've connected quite a few GFCI's and never seen one with a ground terminal; usually only 2 hots and a neutral. However even if this is the case, it probably wont fix your problem.
Replace the element, don't risk your life with electricity.
**update**
Minor progress today. Ripped everything apart and rewired using 12ga instead of 8ga. Problem with tripping out persisted. BUT. I had a thought to try removing my ground wire from the kettle. And the tripping stopped. So now I just need to figure out if I need that ground wire or not, and if so where I went wrong wiring it up. Anyone have any thoughts on this?
The details of my ground is 200 amp panel in the main house uses a 100 amp breaker to feed the garage panel. (4 strand with ground going back to 100 amp breaker in 200 amp panel). And then the kettle gets hooked to the ground lug on the 50 amp gfci in the 100 amp panel.