Okay I have re wired and come up with a schematic.. I am getting ready to test now. Please let me know if you see something wrong.



 
Pull the neutral feed off the "buss strip" and try it. ( in the panel you built)


Sent from my iPad using Home Brew
 
Pull the neutral feed off the "buss strip" and try it. ( in the panel you built)


Sent from my iPad using Home Brew

Okay when I do this the breaker doesn't trip when I push the switches but it doesn't seem to be getting power either... switches don't illuminate and pid doesn't turn on.
 
Nothing to do with the GFCI tripping, but what size wire is going from your 30A breaker to the outlet? Is should be at least #10. From the photo it doesn't look like #10, but the photo could be deceiving.

Also, was a new wire run from the panel to your new outlet? Is all wiring to for the new outlet dedicated to the new outlet? Just thinking out loud if it's possible for the problem to be external from your panel, even though the issue happens when turning the panel on.
 
Nothing to do with the GFCI tripping, but what size wire is going from your 30A breaker to the outlet? Is should be at least #10. From the photo it doesn't look like #10, but the photo could be deceiving.

Also, was a new wire run from the panel to your new outlet? Is all wiring to for the new outlet dedicated to the new outlet? Just thinking out loud if it's possible for the problem to be external from your panel, even though the issue happens when turning the panel on.

It is #10, the wire was existing from dryer outlet with breaker replaced with gfci and receptacle replaced with 4 prong. Everything was installed by a hired electrician.
 
Do you by any chance have a dryer outlet at the wall, with a dryer cord to run your element? If so, try running the kettle plugged directly into the wall.

Your element doesn't use the neutral. The lights will, as will the controller. If the kettle works ok direct from the outlet, then the problem is likely your neutral. I had a similar problem to what you describe, and the problem was the neutral was not run through the GFCI, it was direct to the electrical panel, and the breaker would register a fault every time the neutral was used.
 
Okay when I do this the breaker doesn't trip when I push the switches but it doesn't seem to be getting power either... switches don't illuminate and pid doesn't turn on.


Ok, now we are getting somewhere. Now reconnect the main neutral and disconnect every neutral from a device, one at a time connect a device (ie switch or light) and determine what device causes the trip. Let us know what you get.

PS, we know the lights were not going to work, we are just troubleshooting
 
Ok, now we are getting somewhere. Now reconnect the main neutral and disconnect every neutral from a device, one at a time connect a device (ie switch or light) and determine what device causes the trip. Let us know what you get.

PS, we know the lights were not going to work, we are just troubleshooting

Okay, progress I think... :mug:

I got as far as connecting the switches (tested individually) and both trip the breaker when connected to neutral with nothing else connected (to neutral). I did not try with the PID hooked up directly, I'm guessing this means the short is somewhere in my switch wiring..?
 
Okay, progress I think... :mug:



I got as far as connecting the switches (tested individually) and both trip the breaker when connected to neutral with nothing else connected (to neutral). I did not try with the PID hooked up directly, I'm guessing this means the short is somewhere in my switch wiring..?


Why do you have a neutral going to a switch? Is for a lamp in the switch? If it's for a lamp, remove the bulb and see what happens. Otherwise the neutral should only be going to the temp controller and the pump and maybe your alarm. Only the hots should be switched. What are the red and blue push buttons for?
 
Buy a 5 dollar meter from harbor freight, and use the meter to find your short. As others read this, and they should know having a short like this can be deadly. I'm sorry to be a "safety sally" A little fear is a good thing. I know I'm not going to be Mr popular for posting this. Don't click on the second link if you have a week stomach.
[ame]https://www.youtube.com/watch?v=42Kn9JlXE5w[/ame]
[ame]https://www.youtube.com/watch?v=x8xOtw-ZP3E[/ame]
 
Buy a 5 dollar meter from harbor freight, and use the meter to find your short. As others read this, and they should know having a short like this can be deadly. I'm sorry to be a "safety sally" A little fear is a good thing. I know I'm not going to be Mr popular for posting this. Don't click on the second link if you have a week stomach.
https://www.youtube.com/watch?v=42Kn9JlXE5w
https://www.youtube.com/watch?v=x8xOtw-ZP3E


Relax, were troubleshooting here. The breaker is doing its job, now let us do ours.
 
Just like anything else a breaker can fail. Poping it over and over is not good. I don't mean any disrespect. I don't want the OP to die or any other brewer reading this years later.
 
Just like anything else a breaker can fail. Poping it over and over is not good. I don't mean any disrespect. I don't want the OP to die or any other brewer reading this years later.



Understood, but I myself have said to many on here, if you can't wire your own panel without help from others, you have no business touching anything electrical. The guy who posted his wooden control panel is far more dangerous than this guy. At least it's a UL listed enclosure. The wooden one is a ticking fire starter. I hear you bro, just keeping the carnage to a minimum.
 
The guy who posted his wooden control panel is far more dangerous than this guy. At least it's a UL listed enclosure. The wooden one is a ticking fire starter.
My panel is "wooden" - the only heat being generated is by the SSR's and as long as they are cooled and everything is grounded appropriately, there's no real issues

electical_body-63750.jpg
 
My panel is "wooden" - the only heat being generated is by the SSR's and as long as they are cooled and everything is grounded appropriately, there's no real issues


It's about its ability to keep the failure of a device or conductor from causing a fire outside its enclosure. A ground isn't going to prevent a catastrophic failure. I've done this for a living in nuclear and conventional power plants since I got out of the submarine navy in 2000. There is right and a wrong way to do all things, flying in the middle may get you far but it's only luck.

There is a reason why the national electrical code is written by the NFPA
National Fire Protection Association
 
Why do you have a neutral going to a switch? Is for a lamp in the switch? If it's for a lamp, remove the bulb and see what happens. Otherwise the neutral should only be going to the temp controller and the pump and maybe your alarm. Only the hots should be switched. What are the red and blue push buttons for?

I was following P-Js diagram which shows neutral going to "x1" on each switch and temp controller. It is going to the led indicator in the switch.

The red and blue push buttons are the switches for PID on/off and element on/off. I have them wired accordingly:

23 --> hot "in"
24 --> load "out"
X2 --> 24
X1 --> neutral

These are the push buttons:
http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=303
 
I was following P-Js diagram which shows neutral going to "x1" on each switch and temp controller. It is going to the led indicator in the switch.



The red and blue push buttons are the switches for PID on/off and element on/off. I have them wired accordingly:



23 --> hot "in"

24 --> load "out"

X2 --> 24

X1 --> neutral



These are the push buttons:

http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=303


Ok, I only see 4 places to wire the switch, 2 for the norm closed and 2 for the norm open, where are the lamp terminals?
 
Just like anything else a breaker can fail. Poping it over and over is not good. I don't mean any disrespect. I don't want the OP to die or any other brewer reading this years later.

I appreciate your concern :mug:

I have seen those videos before and have the utmost respect for the dangers of electricity. Before starting this I read as much as possible and felt I understood enough to step outside my comfort zone to learn a new skill. I am proceeding with caution and am very thankful for the concern and helpfulness of trimixdriver1, minbari, and yourself.
 
Possibly, I would have to take the switch completely apart to see...

Should I instead remove the jumpers from 24 -> x2 and disconnect neutral to x1?

I was connecting coil neutral through Element switch x1 also, so I would need to connect coil neutral to temp controller, temp controller to neutral bus, correct?
 
Possibly, I would have to take the switch completely apart to see...



Should I instead remove the jumpers from 24 -> x2 and disconnect neutral to x1?



I was connecting coil neutral through Element switch x1 also, so I would need to connect coil neutral to temp controller, temp controller to neutral bus, correct?


Yes remove wires to X1 and X2

To make it easier, if you have the wire, run a neutral from your terminal strip to each component that needs a neutral.

Also looking at the switch, there is a step down transformer and rectifier each one to go from 120 to 24vdc

There may be some loss that is causing an imbalance and causing the GFCI to trip.
 
Yes remove wires to X1 and X2

To make it easier, if you have the wire, run a neutral from your terminal strip to each component that needs a neutral.

Also looking at the switch, there is a step down transformer and rectifier each one to go from 120 to 24vdc

There may be some loss that is causing an imbalance and causing the GFCI to trip.

I thought these were the standard switches that many electric brewers are using. I rewired the neutral wires as you described and the gfci is still tripping. The problem definitely seems to be the switches... Your advice, sir?
 
Understood, but I myself have said to many on here, if you can't wire your own panel without help from others, you have no business touching anything electrical. The guy who posted his wooden control panel is far more dangerous than this guy. At least it's a UL listed enclosure. The wooden one is a ticking fire starter. I hear you bro, just keeping the carnage to a minimum.

Ha ha, cause no one has wire running through wood in thier house right?
 
I thought these were the standard switches that many electric brewers are using.
They are. I use them in mine and they work great. They are switch and lamp in one, which is why they require a neutral.


I was just looking at your home made diagram again; disconnect just the alarm from the "temperature controller" and try again.


Here is a diagram that is more along the lines of what (I think) you are trying to do. Based on P-Js but using the devices that you are using. (the 2451 wiring matches the one you have).

bwerner.jpg
 
I've read through this thread and it seems like there is only one thing that hasn't directly been proven yet. I think.

In my opinion the next step I would take to prove that the switches are in fact you problem is to remove the load from the switches and leave the lamps in.

So remove your power out from 24, but leave the jumper from 24 to x2 on both switches and leave x1 connected to the neutral. This sheds the load from everything else and will only have the lamp turn on when you push the switch. Also this gives you the ability to test one switch at a time because you have the lamp on only when the switch is closed.

If everything holds, no trip, then do what spkguitar recommended. Reconnect everything as it should be and remove the alarm wires from the pid. Though I really doubt that is causing your problem it is worth a shot.

This would be my next step to prove the switch are or are not your problem.

Good luck dude.
 
Did you ever check the gfci breaker wires to see if they are set up properly. The most common cause of a 240v gfci breaker tripping as soon as power is applied through it is the load nuetral is bonded to the buss bar. It NEEDS to be on the load nuetral of the breaker itself. Very common issue. The permanent white wire coming out of the breaker goes to nuetral buss bar. Nuetral wire from your controller outlet goes to load nuetral on the breaker.
 