Where is the neutral that goes to your outlet coming from? Breaker or bus bar?
Pull the neutral feed off the "buss strip" and try it. ( in the panel you built)
Sent from my iPad using Home Brew
Nothing to do with the GFCI tripping, but what size wire is going from your 30A breaker to the outlet? Is should be at least #10. From the photo it doesn't look like #10, but the photo could be deceiving.
Also, was a new wire run from the panel to your new outlet? Is all wiring to for the new outlet dedicated to the new outlet? Just thinking out loud if it's possible for the problem to be external from your panel, even though the issue happens when turning the panel on.
Okay when I do this the breaker doesn't trip when I push the switches but it doesn't seem to be getting power either... switches don't illuminate and pid doesn't turn on.
Ok, now we are getting somewhere. Now reconnect the main neutral and disconnect every neutral from a device, one at a time connect a device (ie switch or light) and determine what device causes the trip. Let us know what you get.
PS, we know the lights were not going to work, we are just troubleshooting
Okay, progress I think...
I got as far as connecting the switches (tested individually) and both trip the breaker when connected to neutral with nothing else connected (to neutral). I did not try with the PID hooked up directly, I'm guessing this means the short is somewhere in my switch wiring..?
Buy a 5 dollar meter from harbor freight, and use the meter to find your short. As others read this, and they should know having a short like this can be deadly. I'm sorry to be a "safety sally" A little fear is a good thing. I know I'm not going to be Mr popular for posting this. Don't click on the second link if you have a week stomach.
https://www.youtube.com/watch?v=42Kn9JlXE5w
https://www.youtube.com/watch?v=x8xOtw-ZP3E
Just like anything else a breaker can fail. Poping it over and over is not good. I don't mean any disrespect. I don't want the OP to die or any other brewer reading this years later.
My panel is "wooden" - the only heat being generated is by the SSR's and as long as they are cooled and everything is grounded appropriately, there's no real issuesThe guy who posted his wooden control panel is far more dangerous than this guy. At least it's a UL listed enclosure. The wooden one is a ticking fire starter.
My panel is "wooden" - the only heat being generated is by the SSR's and as long as they are cooled and everything is grounded appropriately, there's no real issues
Why do you have a neutral going to a switch? Is for a lamp in the switch? If it's for a lamp, remove the bulb and see what happens. Otherwise the neutral should only be going to the temp controller and the pump and maybe your alarm. Only the hots should be switched. What are the red and blue push buttons for?
I was following P-Js diagram which shows neutral going to "x1" on each switch and temp controller. It is going to the led indicator in the switch.
The red and blue push buttons are the switches for PID on/off and element on/off. I have them wired accordingly:
23 --> hot "in"
24 --> load "out"
X2 --> 24
X1 --> neutral
These are the push buttons:
http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=303
Just like anything else a breaker can fail. Poping it over and over is not good. I don't mean any disrespect. I don't want the OP to die or any other brewer reading this years later.
Remove the leads to the lamps on the switch and report back.
Possibly, I would have to take the switch completely apart to see...
Should I instead remove the jumpers from 24 -> x2 and disconnect neutral to x1?
I was connecting coil neutral through Element switch x1 also, so I would need to connect coil neutral to temp controller, temp controller to neutral bus, correct?
Yes remove wires to X1 and X2
To make it easier, if you have the wire, run a neutral from your terminal strip to each component that needs a neutral.
Also looking at the switch, there is a step down transformer and rectifier each one to go from 120 to 24vdc
There may be some loss that is causing an imbalance and causing the GFCI to trip.
Understood, but I myself have said to many on here, if you can't wire your own panel without help from others, you have no business touching anything electrical. The guy who posted his wooden control panel is far more dangerous than this guy. At least it's a UL listed enclosure. The wooden one is a ticking fire starter. I hear you bro, just keeping the carnage to a minimum.
They are. I use them in mine and they work great. They are switch and lamp in one, which is why they require a neutral.I thought these were the standard switches that many electric brewers are using.