So I got my 30 amp outlet installed, tested the voltage (246v at the receptacle), and plugged my panel in.
I'm using an inline 30 amp GFCI cord from the panel to the outlet. The GFCI has a series of steps to determine its in working order, and it checked out (plug in, press test button, press reset button, look for red flag to appear, continue use if flag appears).
I turned my pump switches on/off and the LEDs light appeared correctly when respective switch was on. I also checked function with two small lamps.
View attachment ImageUploadedByHome Brew1420322141.148385.jpg
I then proceeded to setup the PID and changed the Sn (temp prob setting) to 21 since I'm using an RTD. At this point the PV value was ambient (60) and the SV was 50. I have a 30 amp DP switch wired between the bus/ssr and outlet to cut power to the element if needed. I'm doing all of this without an element plugged in, just trying to verify that each outlet was getting power or not and switch were working. The temp sensor was plugged in though to see if a signal was being sent. Here's pics of the internal wiring.
View attachment ImageUploadedByHome Brew1420322429.021914.jpg
View attachment ImageUploadedByHome Brew1420322352.365683.jpg
View attachment ImageUploadedByHome Brew1420322458.889657.jpg
View attachment ImageUploadedByHome Brew1420322483.909666.jpg
The element switch was in the off position (although in a above pic it is in the on position, I turned it off before programming the PID). To see if the SSR would send power to the outlet and turn the light on, I adjusted the SV up to 65 in hopes the PID would tell the SSR to send power. I then turned the double pole light switch, felt a slight shock and heard a loud pop (and slight burning plastic smell) come from the control box. The GFCI tripped and tripped the 30 amp main panel breaker as well. When I opened the box, the plastic SSR cover was off and charred. The above SSR pic was post "pop" so it didn't expand or pop from its casing, just the cover.
View attachment ImageUploadedByHome Brew1420322986.388269.jpg
The right side is less charred (it's the side allowing power from the bus to the switch) and the left side receives power from the PID. The little red SSR power light is where the circular char is located.
Did I do something wrong? Should I have had the element plugged in? Assuming the SSR is shot and was it faulty?
I've triple checked the wiring and everything is fine correctly according the PJs plan and my understanding. I also reset the breaker (with the DP switch off) and turned the panel back on. The PID and pump switches work as before but I didn't try anything else with the PID temp setting as I just wanted to see if anything else blew.
I'm using an inline 30 amp GFCI cord from the panel to the outlet. The GFCI has a series of steps to determine its in working order, and it checked out (plug in, press test button, press reset button, look for red flag to appear, continue use if flag appears).
I turned my pump switches on/off and the LEDs light appeared correctly when respective switch was on. I also checked function with two small lamps.
View attachment ImageUploadedByHome Brew1420322141.148385.jpg
I then proceeded to setup the PID and changed the Sn (temp prob setting) to 21 since I'm using an RTD. At this point the PV value was ambient (60) and the SV was 50. I have a 30 amp DP switch wired between the bus/ssr and outlet to cut power to the element if needed. I'm doing all of this without an element plugged in, just trying to verify that each outlet was getting power or not and switch were working. The temp sensor was plugged in though to see if a signal was being sent. Here's pics of the internal wiring.
View attachment ImageUploadedByHome Brew1420322429.021914.jpg
View attachment ImageUploadedByHome Brew1420322352.365683.jpg
View attachment ImageUploadedByHome Brew1420322458.889657.jpg
View attachment ImageUploadedByHome Brew1420322483.909666.jpg
The element switch was in the off position (although in a above pic it is in the on position, I turned it off before programming the PID). To see if the SSR would send power to the outlet and turn the light on, I adjusted the SV up to 65 in hopes the PID would tell the SSR to send power. I then turned the double pole light switch, felt a slight shock and heard a loud pop (and slight burning plastic smell) come from the control box. The GFCI tripped and tripped the 30 amp main panel breaker as well. When I opened the box, the plastic SSR cover was off and charred. The above SSR pic was post "pop" so it didn't expand or pop from its casing, just the cover.
View attachment ImageUploadedByHome Brew1420322986.388269.jpg
The right side is less charred (it's the side allowing power from the bus to the switch) and the left side receives power from the PID. The little red SSR power light is where the circular char is located.
Did I do something wrong? Should I have had the element plugged in? Assuming the SSR is shot and was it faulty?
I've triple checked the wiring and everything is fine correctly according the PJs plan and my understanding. I also reset the breaker (with the DP switch off) and turned the panel back on. The PID and pump switches work as before but I didn't try anything else with the PID temp setting as I just wanted to see if anything else blew.