Your actual electricity voltage is probably somewhere between 220v and 250v. It should be the same as all other residential 240v systems in the U.S. The 250V on the receptacle is just its rating. It is not the voltage of your electricity. If you measure the voltage across the two hots of the receptacle you will see your actual voltage (under no load. - It might drop a bit under load). If measure from the ground of the receptacle to either hot you should see 1/2 of the voltage; i.e. ~120v.
Running your Braumeister on this will not damage it because of the type of plug (assuming everything is wired correctly). And as long as the voltage does not exceed the Braumeister voltage rating, everything should work just fine. In fact, you should be better off without the converter.
The Braumeister manual shows '230 V ~'. That means 'approx. 230 V'. I believe U.S. electricity is more properly called 240v (and 120v), but you will hear it referred to as 220, 230, 240, etc. Spiedel says that the Braumeister is designed to run properly with U.S. electricity.
Thank you for putting my mind at ease. Now maybe i can get these guys to make me a cable http://www.elecordset.com/moreinfo.aspx?pid=NEMA10-30P&cs=/products/HeavyDuty.aspx&ai=M
From what i read the Braumeister uses a c13 end, so a nema 10-30p with a c13 female should do the trick.
Then on to installing a vent hood and i can be brewing nearly every day while i do my day job!