Ive decided to make the transition to electric (BIAB) so I can brew in the basement all year round. I havent yet decided on a controller but I have my eyes on the brew boss at the moment. I enjoy DIY projects and I may eventually convince myself to just build my own. Just not sure I want to invest the time.
Anyways, here is my plan so far for getting power to the controller. Would appreciate a critique.
1. My breaker box already has a 40 amp 240V circuit as a prewire for a cooktop. We have a gas cooktop so that circuit will never be used. The wire is 8 gauge. Ill pull it down into the basement and reroute to my brew area. Im going to reuse the wire but Ill swap out the 40 amp breaker for a 30 to protect the 10 gauge wiring in the brew boss (or other controller).
2. I had thought about using a non-GFCI breaker and spa panel, but the cost difference would be minimal vs a 30 amp GFCI breaker. Going with a GFCI breaker seems like the cleaner solution. If I do that, I can then just connect the controller and circuit wiring in a junction box. I dont mind having the controller hard-wired for now. When the basement gets finished and I have a dedicated brew space, I may install a receptacle.
3. I have a blichmann 15 240V boil coil, so whatever controller I use needs to have a twist lock L6-30 receptacle
4. If I go with the 30 amp GFCI breaker, the pigtail gets connected to the neutral bus bar and there are no other neutral/ground connections for the breaker, correct?
5. The existing circuit wiring is 2 hots, neutral, and ground. The brew boss manual says I only need the hots and ground, no neutral. Would I still connect the neutral to the bus bar at the panel, and then just put a wire nut on the neutral at the j-box? Will the GFCI still function correctly this way?
Thanks for the review and advice.
Ive decided to make the transition to electric (BIAB) so I can brew in the basement all year round. I havent yet decided on a controller but I have my eyes on the brew boss at the moment. I enjoy DIY projects and I may eventually convince myself to just build my own. Just not sure I want to invest the time.
Anyways, here is my plan so far for getting power to the controller. Would appreciate a critique.
1. My breaker box already has a 40 amp 240V circuit as a prewire for a cooktop. We have a gas cooktop so that circuit will never be used. The wire is 8 gauge. Ill pull it down into the basement and reroute to my brew area. Im going to reuse the wire but Ill swap out the 40 amp breaker for a 30 to protect the 10 gauge wiring in the brew boss (or other controller).
2. I had thought about using a non-GFCI breaker and spa panel, but the cost difference would be minimal vs a 30 amp GFCI breaker. Going with a GFCI breaker seems like the cleaner solution. If I do that, I can then just connect the controller and circuit wiring in a junction box. I dont mind having the controller hard-wired for now. When the basement gets finished and I have a dedicated brew space, I may install a receptacle.
3. I have a blichmann 15 240V boil coil, so whatever controller I use needs to have a twist lock L6-30 receptacle
4. If I go with the 30 amp GFCI breaker, the pigtail gets connected to the neutral bus bar and there are no other neutral/ground connections for the breaker, correct?
5. The existing circuit wiring is 2 hots, neutral, and ground. The brew boss manual says I only need the hots and ground, no neutral. Would I still connect the neutral to the bus bar at the panel, and then just put a wire nut on the neutral at the j-box? Will the GFCI still function correctly this way?
Thanks for the review and advice.