List of PJ Electrical Diagrams

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
That's awesome!

I did scan this thread and didn't find exactly what I'm looking for but I will give that a once-over.

Thanks for sharing! Austinjs0102
 
This was the one I was talking about. excuse the quality. I had to scan a print-out and then color in the lines with pic editor.

50a Switched.jpg
 
I have been brewing for a couple of years (all grain using propane) and finally starting to gather parts for my electric controller. I went to see if P-J was still posting wiring diagrams and it looks as though I was a bit too late. Started reading the thread and saw that he was not in good health and sure hope he is still around.

Does anyone have a wiring diagram for the following:

I am running a 3-wire/30A (A, B, and Ground) 10 gauge extension cord from a dryer outlet in my basement for the 220v side.
I will also be running a seperate 110v line into the controller to run pumps as well as the Contactor coils.
I will be running two 5500w elements (one at a time using a three-way selector switch).
2 REX-C100-FK02-V*AN PID's
2 Fotek SSR 40A SSR's
3 250v/30a - 110v coil Contactors
I have drawn up a rough wiring diagram. Is there someone that can check my work to see if this can work or not? Add / Change / Subtract?

Thank you in advance!

WORKING 220V and 110V.jpg
 
What are you planning for GFCI protection? Brewing without GFCI represents an electrocution hazard to you.

I recommend you double check the wiring of your dryer outlet to be sure it is really hot-hot-gnd, and not hot-hot-neutral. My understanding is that most are H-H-N.

Note that the FK02 version uses type K thermocouples for temp input, so PT100 RTD's cannot be used. Any probe extension wire needs to be type K compatible thermocouple extension wire. Ordinary copper wire will give you temperature errors.

The SSR output of the C100 is on terminals 4 (+) & 5 (-), not 3 & 4 as you show. http://www.rkcinst.co.jp/english/pdf_manual/imnzc22e1.pdf

Brew on :mug:
 
I have been brewing for a couple of years (all grain using propane) and finally starting to gather parts for my electric controller. I went to see if P-J was still posting wiring diagrams and it looks as though I was a bit too late. Started reading the thread and saw that he was not in good health and sure hope he is still around.

Does anyone have a wiring diagram for the following:

I am running a 3-wire/30A (A, B, and Ground) 10 gauge extension cord from a dryer outlet in my basement for the 220v side.
I will also be running a seperate 110v line into the controller to run pumps as well as the Contactor coils.
I will be running two 5500w elements (one at a time using a three-way selector switch).
2 REX-C100-FK02-V*AN PID's
2 Fotek SSR 40A SSR's
3 250v/30a - 110v coil Contactors
I have drawn up a rough wiring diagram. Is there someone that can check my work to see if this can work or not? Add / Change / Subtract?

Thank you in advance!

Is one of the elements going to be in you boil kettle? If so, the REX C100 does not have a manual output level control function, so is not suitable for controlling boil vigor.

Brew on :mug:
 
Search for images using
"homebrewtalk p-j diagrams"
as search terms and you'll find MANY of his diagrams.
 
What are you planning for GFCI protection? Brewing without GFCI represents an electrocution hazard to you.

I recommend you double check the wiring of your dryer outlet to be sure it is really hot-hot-gnd, and not hot-hot-neutral. My understanding is that most are H-H-N.

Note that the FK02 version uses type K thermocouples for temp input, so PT100 RTD's cannot be used. Any probe extension wire needs to be type K compatible thermocouple extension wire. Ordinary copper wire will give you temperature errors.

The SSR output of the C100 is on terminals 4 (+) & 5 (-), not 3 & 4 as you show. http://www.rkcinst.co.jp/english/pdf_manual/imnzc22e1.pdf

Brew on :mug:

For the Dryer outlet, Since this is not a four-wire, you cannot make a neutral. You have to use it as a ground. Even in my Main Panel, the ground wire is on the ground bar along with all neutrals wired in my house.

<I just watch a video of an electrician installing a GFCI using 3-wire.>
Looks like I will be installing one (I am glad because I don't feel like dying, lol).

For the 110v side, I was told to run a regular 110v into the control panel and use it for my pumps, PID, and coils.

Thanks!:rockin:

IMG_0396.jpg
 
Is one of the elements going to be in you boil kettle? If so, the REX C100 does not have a manual output level control function, so is not suitable for controlling boil vigor.

Brew on :mug:


Could a 220v voltage regulator work in this instance between the contactor and the output to the elements?

Thanks!
 
Could a 220v voltage regulator work in this instance between the contactor and the output to the elements?

Thanks!

Best solution is an SSVR. Kind of like an SSR, but controlled by a potentiometer (variable resistor) to give PWM output. Just be sure you use a high quality potentiometer with the SSVR, as line voltage is connected to the potentiometer (from the SSVR control terminals.)

Brew on :mug:
 
For the Dryer outlet, Since this is not a four-wire, you cannot make a neutral. You have to use it as a ground. Even in my Main Panel, the ground wire is on the ground bar along with all neutrals wired in my house.

<I just watch a video of an electrician installing a GFCI using 3-wire.>
Looks like I will be installing one (I am glad because I don't feel like dying, lol).

For the 110v side, I was told to run a regular 110v into the control panel and use it for my pumps, PID, and coils.

Thanks!:rockin:

It's possible to derive a four wire circuit from a three wire with the H-H-N configuration. If you do this, you don't need a separate outlet to get 120V in your panel. The caveat is that the derived ground might not actually be at earth potential if there are significant currents on the neutral wire (due to 120V loads.) Shouldn't be an issue unless you actually earth ground something connected to the derived ground. The following diagram shows how to connect the GFCI breaker in a spa panel to derive a four wire feed from a three wire, H-H-N feed (yellow is neutral in the diagram.)

Spa Panel w 3-wire feed.jpg

Brew on :mug:
 
It's possible to derive a four wire circuit from a three wire with the H-H-N configuration. If you do this, you don't need a separate outlet to get 120V in your panel. The caveat is that the derived ground might not actually be at earth potential if there are significant currents on the neutral wire (due to 120V loads.) Shouldn't be an issue unless you actually earth ground something connected to the derived ground. The following diagram shows how to connect the GFCI breaker in a spa panel to derive a four wire feed from a three wire, H-H-N feed (yellow is neutral in the diagram.)

View attachment 381894

Brew on :mug:

So, this is NOT SAFE as there is no true ground, correct? Wonder what a professional electrician thinks of this. If it is safe, I would like to speak with someone who is using this exact setup.

I may be moving soon and hoping that there will be a 4-wire 220v to use so I do not have to MacGyver the 3-wire and have a potential to getting killed. I may have to stick with propane until then.

:confused:
 
So, this is NOT SAFE as there is no true ground, correct? Wonder what a professional electrician thinks of this. If it is safe, I would like to speak with someone who is using this exact setup.

I may be moving soon and hoping that there will be a 4-wire 220v to use so I do not have to MacGyver the 3-wire and have a potential to getting killed. I may have to stick with propane until then.

:confused:

I am not a certified electrician, but I consider the arrangement safe (and I'm pretty anal about safety.) I believe P-J first posted this method of deriving a four wire feed from a three wire feed (second post in this thread. Unfortunately the pic in the post has disappeared, but was the same as I posted above.) The GFCI still performs its function to prevent you from getting more than ~5mA of current from a shock. Even if the "ground" isn't at 0 V, it will still shunt and sink any current available from a short to a source at a high enough voltage to be a safety concern. I don't use this arrangement myself, but I know there are several users on HBT.

If you read the thread linked above, you will see all the debate about whether or not this arrangement is safe. I'll throw in some calculations to illustrate what a realistic scenario looks like. With two pumps running at once, plus the miscellaneous low wattage electronics, the total 120V current would be about 5A. Thus the current flowing thru the neutral wire would be 5A. 10AWG wire has a resistance of 1 ohm/1000 ft. If you have a 100 ft run of 10AWG in your installation, the resistance is 0.1 ohm. The max voltage (relative to ground) at the load end of the neutral is 5A * 0.1 ohm = 0.5V. A resistance of up to 2 ohms in the ground path is generally considered acceptable, and the derived ground would be at 5% of that.

Brew on :mug:
 
I am not a certified electrician, but I consider the arrangement safe (and I'm pretty anal about safety.) I believe P-J first posted this method of deriving a four wire feed from a three wire feed (second post in this thread. Unfortunately the pic in the post has disappeared, but was the same as I posted above.) The GFCI still performs its function to prevent you from getting more than ~5mA of current from a shock. Even if the "ground" isn't at 0 V, it will still shunt and sink any current available from a short to a source at a high enough voltage to be a safety concern. I don't use this arrangement myself, but I know there are several users on HBT.

If you read the thread linked above, you will see all the debate about whether or not this arrangement is safe. I'll throw in some calculations to illustrate what a realistic scenario looks like. With two pumps running at once, plus the miscellaneous low wattage electronics, the total 120V current would be about 5A. Thus the current flowing thru the neutral wire would be 5A. 10AWG wire has a resistance of 1 ohm/1000 ft. If you have a 100 ft run of 10AWG in your installation, the resistance is 0.1 ohm. The max voltage (relative to ground) at the load end of the neutral is 5A * 0.1 ohm = 0.5V. A resistance of up to 2 ohms in the ground path is generally considered acceptable, and the derived ground would be at 5% of that.

Brew on :mug:


Thank you! Great information.

If anyone reading this has a similar setup, I would like to discuss.

Much appreciated!
 
Note that the FK02 version uses type K thermocouples for temp input, so PT100 RTD's cannot be used. Any probe extension wire needs to be type K compatible thermocouple extension wire. Ordinary copper wire will give you temperature errors.

Hi Doug293cz ~ Will the PT100 RTD's be compatible with the Auberin SYL-2352 PID's? Since I will need to replace the REX-C100's I will need to know if I will need to replace the sensors. Thanks!
 
Hi Doug293cz ~ Will the PT100 RTD's be compatible with the Auberin SYL-2352 PID's? Since I will need to replace the REX-C100's I will need to know if I will need to replace the sensors. Thanks!
Yes, PT100 RTD's will work with the Auber SYL-2352.

If you are going to get new controllers, I strongly recommend you consider the Auber EZBoil DSPR120 or DSPR300 (the 300 has alarm functions that the 120 does not.) They are also compatible with PT100 RTD's. The DSPR's perform the same function as a PID, and they also provide twist knob boil power control. The DSPR's temp control function works better than PID's for a mashing application. They are more stable, and much less difficult to tune (if they even need tuning.)

Brew on :mug:
 
Yes, PT100 RTD's will work with the Auber SYL-2352.

If you are going to get new controllers, I strongly recommend you consider the Auber EZBoil DSPR120 or DSPR300 (the 300 has alarm functions that the 120 does not.) They are also compatible with PT100 RTD's. The DSPR's perform the same function as a PID, and they also provide twist knob boil power control. The DSPR's temp control function works better than PID's for a mashing application. They are more stable, and much less difficult to tune (if they even need tuning.)

Brew on :mug:

Much appreciated! I will look into that version.
 
Tried to open some of the wiring diagrams but couldn't get them to open. Going to build a BIAB setup with an Inkbird pid and a single pump with a 5500w single element. Any help is appreciated.
TIA
 
Tried to open some of the wiring diagrams but couldn't get them to open. Going to build a BIAB setup with an Inkbird pid and a single pump with a 5500w single element. Any help is appreciated.
TIA
Before you buy any PID, you should look at the Auber Instruments EZBoil controllers (DSPR120 and DSPR300.) They perform the same function as a PID with manual control option, but they are easier to use and more stable than PID's. Pretty much everyone on HBT that has experience with both agrees that the EZBoil is a better choice than a PID. The EZBoil is a bit costlier than a low end PID, but if you look at the entire budget for an electrified system, the extra cost is a very small fraction of the total.

Since the P-J diagrams are getting harder and harder to find, I offer you this for consideration. You can leave out one of the pump switches and outlets, since you will only have one pump. If you want different functionality, that can be accommodated. This design has interlocks that prevent you from turning on the system if the pump or element is turned on (no surprises when you flip the main power switch.) Simpler (and cheaper) designs are possible, but they have more operator error failure modes available.

DSPR300 2-Pump 240V dual contactors safe-start rev-2.jpg

Of course the DSPR could be replaced by a PID if that's what you really want to do (terminal assignments will be different.) Other components can be substituted with equivalents as long as the voltage and current ratings are no lower than the listed components.

Brew on :mug:
 
Before you buy any PID, you should look at the Auber Instruments EZBoil controllers (DSPR120 and DSPR300.) They perform the same function as a PID with manual control option, but they are easier to use and more stable than PID's. Pretty much everyone on HBT that has experience with both agrees that the EZBoil is a better choice than a PID. The EZBoil is a bit costlier than a low end PID, but if you look at the entire budget for an electrified system, the extra cost is a very small fraction of the total.

Since the P-J diagrams are getting harder and harder to find, I offer you this for consideration. You can leave out one of the pump switches and outlets, since you will only have one pump. If you want different functionality, that can be accommodated. This design has interlocks that prevent you from turning on the system if the pump or element is turned on (no surprises when you flip the main power switch.) Simpler (and cheaper) designs are possible, but they have more operator error failure modes available.

View attachment 382855

Of course the DSPR could be replaced by a PID if that's what you really want to do (terminal assignments will be different.) Other components can be substituted with equivalents as long as the voltage and current ratings are no lower than the listed components.

Brew on :mug:

Doug thanks for posting this wiring diagram, this is just what I have been looking for. Im going make a order to Auber and was wondering if you would recommend parts # for the main power witch and alarm. thanks for all the help to the community.
 
Doug thanks for posting this wiring diagram, this is just what I have been looking for. Im going make a order to Auber and was wondering if you would recommend parts # for the main power witch and alarm. thanks for all the help to the community.
The Auber key switch (Main Power Switch) is the SW8 (http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=277.) Doesn't matter if you order the 1NO/1NC or 2NO option, as we only use 1NO block in this design.

The alarm is the FLBuz (110V option, http://www.auberins.com/index.php?main_page=product_info&cPath=7_33&products_id=215) or the FLBuz-120-16 (http://www.auberins.com/index.php?main_page=product_info&cPath=7_33&products_id=221.)

The design calls out either SW1 (push button) or SW16 (rotary) lighted switches for the Element Enable and Pump switches. SW1 is incorrect (as they are 2 NO blocks) and the design requires SW11 (which are 1NO/1NC, http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=303.) If you use SW16's, you need to specify the 1NO/1NC option (http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=349.)

Brew on :mug:
 
The Auber key switch (Main Power Switch) is the SW8 (http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=277.) Doesn't matter if you order the 1NO/1NC or 2NO option, as we only use 1NO block in this design.

The alarm is the FLBuz (110V option, http://www.auberins.com/index.php?main_page=product_info&cPath=7_33&products_id=215) or the FLBuz-120-16 (http://www.auberins.com/index.php?main_page=product_info&cPath=7_33&products_id=221.)

The design calls out either SW1 (push button) or SW16 (rotary) lighted switches for the Element Enable and Pump switches. SW1 is incorrect (as they are 2 NO blocks) and the design requires SW11 (which are 1NO/1NC, http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=303.) If you use SW16's, you need to specify the 1NO/1NC option (http://www.auberins.com/index.php?main_page=product_info&cPath=7_32&products_id=349.)

Brew on :mug:

thanks for the info and the clarification on the witches
 
so... what is the best way to attach the smaller diameter wires to the large wires for things like the fuses and the indicator light?
thanks!

1-PID%201-Element%200-Pump%200-Aux%20240V%20only%20simple.PNG
 
so... what is the best way to attach the smaller diameter wires to the large wires for things like the fuses and the indicator light?
thanks!

Terminal (or bus) strips/blocks are a good option, as pointed out by @highland_brewer. On images.google.com, search for "terminal block and jumper". You should be able to figure out how these work by looking at some of the images. Need to make sure that you buy strips/blocks rated for 240V/30A (or higher.)

You can also arrange your wire routing to put two spade or eyelet crimped wire terminations on a single device terminal like is shown in the design in this post. If you don't fully understand the design's connectivity, and how to move wires without changing the connectivity, then terminal strips are a better choice.

Brew on :mug:
 
thanks everyone... now, the next question...using the diagram I posted above... will this SSR be wired just like it looks in the diagram? It doesn't have the "1-2-3-4" but instead has "L1-L2-T1-T2"...

teledyne relay.jpg
 
thanks everyone... now, the next question...using the diagram I posted above... will this SSR be wired just like it looks in the diagram? It doesn't have the "1-2-3-4" but instead has "L1-L2-T1-T2"...

NO. This is a dual SSR (two SSR's in one package.) The screw terminals are all AC power connections. The left side is for one SSR, and the right side for the other. The DC control signals go to the pins near the bottom center (above the mounting hole.) I don't know which pins control which SSR, or which are plus or minus. It may be marked on the body somewhere (like the AC connections are), or you may have to look for the information on the interwebs.

Edit: Looking harder at the pic, the control signal pins are marked (just above the pins.)

Brew on :mug:
 
thanks again. I wondered what the pins were... I guess they require special connectors...maybe I should just pick up a regular MGR-1D4840?
The pins are marked from top to bottom with -/+ 2 on top pair and -/+1 on the bottom pair.
Bob

NO. This is a dual SSR (two SSR's in one package.) The screw terminals are all AC power connections. The left side is for one SSR, and the right side for the other. The DC control signals go to the pins near the bottom center (above the mounting hole.) I don't know which pins control which SSR, or which are plus or minus. It may be marked on the body somewhere (like the AC connections are), or you may have to look for the information on the interwebs.

Edit: Looking harder at the pic, the control signal pins are marked (just above the pins.)

Brew on :mug:
 
thanks again. I wondered what the pins were... I guess they require special connectors...maybe I should just pick up a regular MGR-1D4840?
The pins are marked from top to bottom with -/+ 2 on top pair and -/+1 on the bottom pair.
Bob

I have never actually had one of these dual SSR's so can't be sure of what size the pins are, but would be very surprised if they were anything other than 0.025" square pins, as these are pretty standard. If they are 0.025" sq pins, you can connect to them with "DuPont" connector jumpers. Just cut the connector from one end, solder to the SSR signal wire coming from your temp controller, and protect the solder junction with some shrink tubing.

Brew on :mug:
 
Last edited by a moderator:
OK...so I found an old computer with a nice RGB 4 pin connector that fits the SSR pins ... which 2 screws on the SSR do I use? the top 2 are marked L1 and L2, the bottom screws are marked T1 and T2. Then, which of the 4 pins do I run to the PID?
thanks!
 
OK...so I found an old computer with a nice RGB 4 pin connector that fits the SSR pins ... which 2 screws on the SSR do I use? the top 2 are marked L1 and L2, the bottom screws are marked T1 and T2. Then, which of the 4 pins do I run to the PID?
thanks!

Everything marked "1" goes with one SSR (L1, T1, etc.), and everything marked "2" (L2, T2, etc.) goes with the other SSR.

Brew on :mug:
 
thanks again... does it matter which way the SSR is wired as far as the T1 and L1 (input/output wise) ?
 
got it... I will attach the energized wire coming from my switch to the L1 terminal, and the wire going from the SSR to my heating element will be connected to the T1 terminal. I will run from the DC "1+" SSR post to the #6 terminal on the PID and the DC "1-" will go to the #7 terminal on the PID...
thanks again. I owe you all a cold one.
:mug:

1-PID%201-Element%200-Pump%200-Aux%20240V%20only%20simple.PNG
 
Now that I have finally settled on my eBrew setup I see that I was a bit too late to utilize PJ's drawings. I managed to save a few but they where the Rims versions and I have decided ultimately on a Herms set up. The closest I could find was the one attached below however I am thinking I could modify it to use the DPSR120 EZ boil and switch the mash and boil functions to control the HLT for mashing and then the BK during the boil with the dial adjust. I would just need to switch the rtd probe from the mash recirc to the boil kettle. The HLT pid would just get my strike water to temp effectively. Eliminating the separate MT Pid (and Timer, not needed)would save a few bucks and fit in the 12 X 12 enclosure I already purchased from Auber

Basically;

HLT Pid (SYL-2532) controls HLT strike water
MLT/Boil (DPSR-120) with switch control for Mash control and Boil Kettle for Boil

Does anyone see an issue going this route and any chance someone has a diagram closer to what I have eliminating the MASH Pid?

LTB 30 amp eBrewery schematic.jpg
 
Now that I have finally settled on my eBrew setup I see that I was a bit too late to utilize PJ's drawings. I managed to save a few but they where the Rims versions and I have decided ultimately on a Herms set up. The closest I could find was the one attached below however I am thinking I could modify it to use the DPSR120 EZ boil and switch the mash and boil functions to control the HLT for mashing and then the BK during the boil with the dial adjust. I would just need to switch the rtd probe from the mash recirc to the boil kettle. The HLT pid would just get my strike water to temp effectively. Eliminating the separate MT Pid (and Timer, not needed)would save a few bucks and fit in the 12 X 12 enclosure I already purchased from Auber

Basically;

HLT Pid (SYL-2532) controls HLT strike water
MLT/Boil (DPSR-120) with switch control for Mash control and Boil Kettle for Boil

Does anyone see an issue going this route and any chance someone has a diagram closer to what I have eliminating the MASH Pid?

Seems like you would want to switch between two temp sensors on the controller for the HLT element. One in the HLT for heating strike/sparge water, and the other in the MLT to control mash temp. Otherwise, you need to figure out ahead of time what HLT temp to set to maintain your desired mash temp, and the offset would likely change for different batch sizes. Either way you need to be able to measure the temp in the MLT during the mash. I would use an EZBoil for both the HLT and BK element control. An interlock to make sure the HERMS recirc pump is on when controlling the mash temp might be a good idea. One concern with switching sensors on a single controller, is that the sensors may need different offset adjustments. I would input the offset for the MLT probe into the controller, and then just determine what the error for the HLT probe is at that offset, and figure that in when setting the temp for strike/sparge water.

Brew on :mug:
 