I have been working on my control panel the last few weekends and am interested to know what you guys think. I still need a way to attach my Thermocouples and another piece of din rail.

IMG_20140824_155819.jpg


20140824_180736.jpg


20140824_180712.jpg


20140824_180705.jpg
 
That looks great you get an (A). Now grasshopper, wire like the wind, (keep everything tight, because that is going to be a stuff job).
 
Looks awesome!

What are those four black components to the right next to the relays and breakers?
 
SSR have a much higher switching speed, but requires a heatsink. Also SSR usually fail shorted.(that's not an advantage)
 
Are you concerned that the heat sinks are inside the box? Where will the heat go - unless you are planning on putting in a fan? I'm just finishing up my own box and reading Kal's design made me design with an external heatsink. I have not brewed yet (soon) In the few tests I've run suggest that my 30A rig generates some serious heat.

Nice layout, neat wiring - neater than mine for sure.

Mike


Sent from my iPad using Home Brew
 
Those heat sinks are going to get pretty hot in that enclosure. You might want to think about a fan and a vent. And have some spare SSR's handy.
 
Those heat sinks are going to get pretty hot in that enclosure. You might want to think about a fan and a vent. And have some spare SSR's handy.
Spare PIDs too. Heat greatly reduces the lifespan of electrolytic capacitors (which are found in most electronic devices, including PIDs).

Kal
 
X2 on the venting. With no fresh air, the heat sinks won't function long term
 
It is important to be aware of heat buildup inside the panel.

But remember that panel is steel, and it will conduct heat away from the SSR's and radiate it into the room without fans

Were it mine, I would mount the SSR's to the box interior so the box becomes the heat sink.
 
I have a 50 amp, 240 vac system. I run two 4500 watt elements in both my HLT and BK. My heat sinks are mounted to the back panel. Granted my heat sinks are bigger and my enclosure is bigger (20X16X8), but I have no ventilation system and my SSRs barely get warm. I have had the same Crydom (40 amp) SSRs for 8 years with no failures. I have replaced one Omega PID but I purchased it used. The size of the heat sink and enclosure will make a significant difference so my situation is not universally applicable. YMMV.
 
I have 50 amp Teledyne ssrs with a decent sized external heatsink. The heat sink gets pretty freaking warm to the touch. Uncomfortablly warm. My power runs hot many day though so that could play a part? 245 volts under a load.
 
I also have two4500w elements but I use two cheapo SSR's (one fatek and one mypin. I use the $3 ebay heatsinks inside my small 12 x 12 x 6 enclosure and a 12v 60mm pc fan which blows through them.... mine stay fairly cool to the touch and have worked well for 10 months now and just over 30 brew sessions.
just added another fotek ssr for my small 1000w rims tube.
 
Shouldnt get so hot you cant touch the heatsink. I have (2)1500watt elements in my bk, each with a 10 amp ssr. I use a pair of pc cpu heatsinks with an 80mm fan on each. Barely gets warm
 
I have a 50 amp, 240 vac system. I run two 4500 watt elements in both my HLT and BK. My heat sinks are mounted to the back panel. Granted my heat sinks are bigger and my enclosure is bigger (20X16X8), but I have no ventilation system and my SSRs barely get warm. I have had the same Crydom (40 amp) SSRs for 8 years with no failures. I have replaced one Omega PID but I purchased it used. The size of the heat sink and enclosure will make a significant difference so my situation is not universally applicable. YMMV.

Would you mind posting a pic of your situation? Trying to make my mind up about which way to go.
 
I have a question about the mech relays. If the SSR's control the mech relays, and the SSR's fail hot, then won't they just energize the mech relays when they fail?
 