I'd make two trips with 5 gallon buckets.
bovineblitz said:If I wanted to be really gangster about it... I'd run hard piping down to the basement, attach a CFC or plate chiller, and go from hot in the garage to pitchable in the basement. It'd be fairly quick to clean since you could do both the chiller and piping at the same time.
I was just starting to look at indoor combustion brewing. Granted there are some specific issues that need to be addressed, but I don't see them as insurmountable.
What am I missing?
Criteria:
Natural Gas conversion kit. No LP, no tanks. No way.
Hard pipe the gas, with appliance shut off valve.
Floor space with a minimum of 30" clear in all directions to all surfaces.
Provide a UL 2 hour rated wall around the room. (2 layers of type x 5/8 drywall each side)
Provide a UL 2 hr ceiling. (Not sure offhand but roughly 3 layers of type x)
Metal hood over convection area.
CO detector & smoke detector - hardwired and battery backup.
Exhaust fan capable of burner BTU / 100 = CFM. Figure a Blichman Top Tier rated at 60,000 BTU with nat gas kit. So that's 600 CFM x 10% factor of safety = 660 CFM exhaust required. That's like two air changes a min for a 10'x12' brew room. Grainger has one that's roughly 800CFM @ 0 head for $180.00
Supply air - probably supply a little less to get negative pressure in brew room. SWMBO doesn't like hops like I do...
Other than drywalling the ceiling which I HATE... this doesn't look too bad / expensive. What am I missing that pushes indoor people to electric?