??? Vey puzzling indeed.
How about when it come to the high temp (about when the GFCI trips) some liquid might have leaked through the element mounting seals into the element connection chamber. It wouldn't take much water to give it a GFCI trip to ground path.
Ok... Ok... I'm grabbing at straws too. But maybe worth a check anyway.
P-J
I wonder if that element can handle the fast switching we normally use on the camcos and the like. It might be something as simple as adjusting the on/off timing in the pid. But who knows.
Since you say it only happens at boil it makes me think it's happening when the ssr goes from on all the time to suddenly switching on and off. And in duty cycle mode it's more of a pwm type of scenario. What your actually doing is switching on and off so fast that the times on as opposed to off determine the duty cycle 80% means it's on for 80% more cycles than its off. Where with an analog manual control you are actually determining the voltage by resistance so an 80% means that your passing 80% of your potential voltage.
But. The GFCI will only trip under 2 conditions:
When there is a power overload beyond the amp range of the breaker (this in not happening).
And when there is a milliamp leakage current from either hot OR the neutral to equipment ground.
But. The GFCI will only trip under 2 conditions:
When there is a power overload beyond the amp range of the breaker (this in not happening).
And when there is a milliamp leakage current from either hot OR the neutral to equipment ground.