This isn't the exact page that Bernie pointed me to, but it has the info on it:

http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/FeederSecondaryTapRules~20020326.htm

Feeder Tap Rules
10-Foot Feeder Tap Rule [240.21(B)(1)]
Feeder tap conductors can be run not over 10 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 1
(1) The ampacity of the tap conductor is:
1 Not less than the computed load in accordance with Article 220, and
2 Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the equipment they supply.
(3) The tap conductors are installed in a raceway if they leave the enclosure.
(4) The tap conductors have an ampacity of no less than 10 percent of the ampacity of the overcurrent protection device from which the conductors are tapped.
 
Actually... it's legit to do this. Bernie Brewer pointed me to a section of the NEC that describes "feeder taps" when I was asking him about whether I could or could not do this sort of thing.

As long as the smaller gauge wire immediately connects to an over current protection device that is properly sized for the smaller wire, it's A-OK to do. There are other rules related to whether the feeder wire is or is not running a long distance or whether it needs to travel through conduit and other stuff, but for short jumps within a single enclosure, most of the rules don't even apply.

I was very thankful for that, too, because I had 50A coming in and wanted to drop down to 25A for my element and 15A for my controls, and the thought of running a big thick-ass wire from the distro block to the panel where my 15A breaker is installed did not thrill me.

Crap... wish I'd known that:

IMG_3354.jpg
 
This isn't the exact page that Bernie pointed me to, but it has the info on it:

http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/FeederSecondaryTapRules~20020326.htm

Feeder Tap Rules
10-Foot Feeder Tap Rule [240.21(B)(1)]
Feeder tap conductors can be run not over 10 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 1
(1) The ampacity of the tap conductor is:
1 Not less than the computed load in accordance with Article 220, and
2 Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the equipment they supply.
(3) The tap conductors are installed in a raceway if they leave the enclosure.
(4) The tap conductors have an ampacity of no less than 10 percent of the ampacity of the overcurrent protection device from which the conductors are tapped.

That is very helpful information, Walker. Thanks!