So to check what Doug is saying. Lift the connections coming off point 2. That will eliminate line to line. But this will allow the control power to turn on the main contactor. If you lift line 2 connection and if it still trips you have a line to neutral problem.I think the problem is more likely a power to power or power to neutral short. If anything were shorted to ground, it should trip the GFCI. GFCI's are designed to trip faster than normal breakers (since people get hurt much quicker than wires, and GFCI's are to protect people, and breakers are to protect wires.)
Brew on![]()
In most cases, "in" vs. "out" doesn't matter for a mechanical switch. If using a double throw switch for selection purposes, then what's connected to what can make a big difference.Just to rule out another potential problem: switches and relays dont care about polarity right?
So to check what Doug is saying. Lift the connections coming off point 2. That will eliminate line to line. But this will allow the control power to turn on the main contactor. If you lift line 2 connection and if it still trips you have a line to neutral problem.
Can't hurt to try.Instead of removing all of the line 2 connections, could I just remove the line 2 supply wire where it comes into the box to the same effect? Then, test it that way to rule out hot to hot shorts?
so one important question, do you have a 4 wire breaker box with an isolated ground ??
I thought ground and neutral were normally bonded in the main service panel (as in the panel shown.)you need to check the main panel , see this panel where the ground and neutral wires are hooked together, this is what I call a 3 wire box, a 4 wire box will separate the copper and white bus bar and the copper will have a wire going into the earth
View attachment 580879
I disagree, I believe you can do a four wire, with or w/o GFCI, in that panel. For no GFCI, the ground and neutral wires both connect to the same bus in the panel. For a GFCI, the load side neutral connects to the neutral terminal on the GFCI breaker, and the GFCI pigtail connects to the common bus, as does the load side ground.its a little tricky and in reality they do join at some point but on the post 1975 breaker boxes they have an isolated ground bar that grounds to earth as well as a neutral and ground to outlets, the above box is like mine and will only work with 3 wires, that 4th wire is that ground to earth in the breaker box and the ground fault and sub panel has to use it, you can also wire a ground fault to a 3 wire box but it's wired different
That design has a hard wired ground fault. It's not gonna work with a properly wired GFCI on the supply side of it. And if you modify the GFCI wiring so it will work, you might as well leave the GFCI out altogether, as it will not provide any ground fault protection.for reference this is a box I made for someone recently, it works with the breaker box I showed above
View attachment 580894
So, you're saying I could just move the ground lug attached to the appliance enclosure off the ground supply wire and attach them to the line 2 supply wire instead? Am I understanding that right?
I'm having a hard time understanding exactly what you are proposing, but if you are saying what I think you are saying, then NO.
Are there advantages to adding an 8 foot ground pole inslead?
Let me see if I have your structure wiring correct:
Is all of the above correct? Is your sub-panel in a separate building from the main panel?
- Your main service panel (the one where the power comes in from the utility) has a 30A, non-GFCI breaker.
- You had a sub-panel added in your brewing area that contains a 30A, GFCI breaker.
- The wiring from your main panel to your sub-panel is 4-wire, fed from the 30A breaker in the main panel.
- Neutral and ground are bonded (connected) together in your main panel.
- Neutral and ground are isolated from each other in your sub-panel.
- There is a 4-wire cable from your sub-panel to your 4-slot outlet.
Note: I think I was confused earlier, and thought your first panel was plugged into a 3-slot outlet.
Brew on![]()