I'm getting different answers from people around me so wanted to check here.
I'm wanting to run a 220v 4500W heating element. It's all located about 8' away from the main breaker panel and the heating element MAY be running for up too 2 hours straight, nothing else running on this breaker. My plan was to run 10/2 wire off a 30amp breaker but I'm being told by a couple people, that I shouldn't run any less then #8 wire and a 50 amp breaker. Someone else is telling me that if I go with a 50amp breaker that it will be a fire hazard because if something goes wrong with the wire getting hot or something, it won't flip the breaker.
The element is only going to be about a 21 amp draw, so don't see the need for a 50 amp breaker. Can someone PLEASE shed some light on this.......
Thanks
I thought it might be nice to go back to the original question.
Running 10g wire off a 30 amp breaker in the main panel is what I'd expect to see for 4500 or 5500 watt elements. You MAY be able to get away with 12 gauge and 20 amp breaker for 4500w but frankly you might as well commit to 5500 watts as the price differences between said breakers, wire and panel components is negligible but the performance of the extra 1000 watts is noticeable.
If you do run 10g wire, then you should not use a 50 amp breaker in the main panel because you CAN overheat the wire without tripping the breaker. If you DO plan to put a 50 amp breaker in, for purposes of future growth and use of two 5500w elements at the same time, then you should use 6 gauge wire.
Other things... Whatever amperage you plan to use, look for a used or surplus GFCI breaker for your main panel and if it's more than $100, consider using a spa disconnect panel inline with your wire run.
If you use wire that has two hots and a ground, you will not be able to derive 120 volts in your control panel for pumps or other 120v accessories unless you run a separate 120v input. Running 240v and 120v items on the same entry cable requires 4 wires, hot, hot, neutral and ground.
It sounds a bit like you want to direct wire an element right to the panel breaker but I really don't recommend it. You should have a fast and convenient way to regulate both on/off functions and power output.
I think that's it, and should provide ample fodder for the garage mechanics and intellectuals alike.