A 50A GFCI breaker may not be such a bargain. You need to wire with 6AWG for 50A vs. 10AWG for 30A. To use 10AWG wiring with a 50A breaker, you need to have a 30A breaker upstream of the 50A'er (in which case the 50A device is only being used for the GFCI functionality.)
Brew on
Naw, you only need #8 THHN for a 50 amp protected load center... Remember, you size the 'wire' according to the load it will be supplying, which can only be 80% of the wire's rated ampacity... The breaker is only protecting the wire and has nothing to do with the load.. Size the wore to 125% of the load, and then size the breaker to the wire it is protecting..
The load center will be for bringing power out to the screened porch which will feed several outlets inside and outside the porch, the brew system, lighting for the porch and outside the porch and a feed out to the picnic area under the firs and cedars, where I'm working on slowly leveling it all out, putting in a big firepit, stone grill/smoker/pizza oven, a concrete picnic table with SS wells in the middle for ice and beverage, a water feature, lighting, and a sound system... Even running a 2" PVC line out there for a 24ch snake so I can set up my mixer out there and jam with friends on the deck I'm building outside the porch... more labor to do all this than money...
:rockin:
It's part of the 20 year plan.. lol... When you don't have a lot of money, you have to go so slow so you have a lot of time to plan (and collect rocks for the grill and stuff)...
It's all part of the master plan... Hope I live long enough to see it!
Just so you know, #8 THHN is rated for 45 amps.. When the wire ampacity does not correspond to available breaker sizes, you are allowed to use the next larger size breaker that does exist... in this case 50A.. The code lists all the sizes breakers come in...
Also, FYI, you are allowed to downsize the neutral on 3 wire 240v feeder circuits... actually, this is legal on 120/208 and 277/480v 3 and 4 wire feeder circuits too.... (not on branch circuits though), so I could even go with #10 there, but I probably won't do that as I have miles of scrap wire around here to use for the feeder...
I'll be putting a regular 30A 2P breaker in the load center on the porch to feed an outlet for the brew system... The 50A GFI will be in the panel in the house that feeds the load center...