But you could put in the thicker wiring suitable to carry 60A, which would be 4-gauge wire and may break the bill if it's any more than a few feet.
I'm running a 60-amp breaker at the main panel that is feeding my sub-panel. I used 6-gauge wire to run from there to the sub-panel. Had an electrician friend work on this with me.
I'm feeding a 5500-watt brewing element, a 5000-watt garage heater, and two 20-amp circuits (though neither is close to 20 amps in terms of the load).
That's 22.91 amps for the element, 20.83 amps for the heater, my Penguin draws 3.75 amps (450 watts but there's probably a little surge on startup), and the RIMS element draws 13.33 amps. All together that's 60 amps plus, which exceeds the breaker feeding the subpanel.
BUT...I'm never running the 5500-watt boil element at the same time as the RIMS. The most I'd ever run simultaneously is the boil element, heater, and Penguin, which totals 47.49 amps on a 60-amp sub-panel w/ 60-amp breaker.