STEEEERIKE 2!
Nope, "'ground' is generally where the missing current goes" is not correct. A GFCI can fail spectacularly with all sorts of effects! If you have never visited his site, Mike Holt has all sorts of great, practical explanations about how stuff works etc.
Understand that you can "over-amp" a GFCI and not break the connection or induce a differential to ground to trip it. That is why you still have to use a circuit breaker, it protects against overload.
G-Ground F-Fault C-Circuit I-Interrupter, no load protection natively.
I was not referring to a device failure situation, but generally what happens when it is doing what it is supposed to...
Generally, when a person comes in contact with electricity and gets shocked, they become/create a circuit between themselves and ground.. Second most likely scenario is hot and neutral, third, would be separated load and line side of a neutral that is part of a balanced 3 wire system with the other circuit still energized (which would trip a GFI just by it's mere existence).. Other scenarios can be between hot and the neutral of another circuit than it's own, or hot and the other phase of a 240v system, or hot and the other phase connected to another circuit altogether..
As you can see, there are a lot of ways a person can become part of the circuit.. and the point I was making in explaining how a GFI works, is that if it only looked for a fault to ground, then it would only protect the person when they experience the first scenario.. becoming a circuit between hot and ground..
That's why it compares current flow in the 'two' conductors to each other.. to protect in almost all of the other scenarios I listed... and more...
Current is equal in all parts of a series circuit... So, unless it goes somewhere else outside of the circuit, what goes out should be the same as what comes back.. 2 amps in the hot leg = 2 amps in the neutral leg (or the other phase in a 240v circuit)
Think of it as a device with two ammeters, one in each of the current carrying legs.. It is constantly looking to see if the two ammeters are reading exactly the same.. How much is going through them is immaterial.. They must always be the 'same' as each other... That's what it measures..
If they are not the same, then that means something has 'tapped in' to the circuit and is finding another path to balance the circuit.. be it ground, an opposite phase on an uninvolved circuit, a neutral being used on a different circuit, whatever...
The only thing it can not detect, is if you become part of the circuit across the two legs it is monitoring/comparing.. Because then you are just a load like anything else, and current out still equals current return...
Does that help you to understand?
Device 'failure' is an entirely different subject.... and so is an over current protection device, or the over current protection part of the GFI...
Imagine a shunt trip device connected to a circuit measuring the difference between the ammeters.. if they are the same, then there is no differential, no trigger voltage, and no trigger for the shunt trip.... but if they are different, then a voltage divider network is created, the shunt trip circuit sees the voltage created by the differential, and triggers the shunt trip..
That is essentially what is happening....