I am still deciding where I will purchase pid's for a control panel build I recently found a link to ebrew supply and have been browsing their line diagrams https://ebrewsupply.s3.amazonaws.com/schematics/30a-2E-BCS-Kit-2014.pdf I notice they have a #6 cu at the beginning of their diagram being that they are feeding one 5500 watt heat element and possibly a pump. I don't see the need. Code allows you to run #10 up to 40 amps so even at 80% of full load it's only 32 amps. Not to mention your breaker is rated at 30 amps. The most you should draw is 30 amps. I am open to being safe I just don't see the need for a no 6 copper. What am I missing