DSPR300 Alarm Wiring

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

cchristoph

Active Member
Joined
Jan 30, 2021
Messages
28
Reaction score
13
I have a DSPR300 I'm using to build an ebiab setup. I want to wire both alarm relays to the same buzzer and kill switch. The switch I'm using is an illuminated 120v switch with three spades Line/Load/Neutral. With the switch line wired to hot bus and neutral wired to neutral bus will it work if I hookup this way?

Auber terminal 2&14 -> buzzer -> load terminal of switch
Auber terminal 1&3 -> neutral bus

Thanks in advance for any guidance.
 
1635998895516.png

You want 1 & 13, not 1 & 3, connected together (pinout of DSPR300 is same as DSPR320.) The way you want to wire it will have the switch light up when the alarms are armed, whether activated or not.

Brew on :mug:
 