I am using this diagram for my control panel.
http://www.pjmuth.org/beerstuff/images/Auberin-wiring1-a11a-SWA-2451-5500w.jpg
The only difference is I have two syl-2352 PID's from Auber. I don't have power to my element outlet for my HLT. I have 120v on both leads on the input side of the contactor but only get a little over 1 volt on the output sides. My BK contactor works fine and I have power all the way to the outlet. I also hear a click when I turn on the power to my BK but nothing when I turn on the HLT. I hooked up the switch for my BK to the contactor and still nothing so I know it is not the switch. I checked continuity from my SSR's to the PID's and that is fine so I know it is not a connection there. Any ideas?
http://www.pjmuth.org/beerstuff/images/Auberin-wiring1-a11a-SWA-2451-5500w.jpg
The only difference is I have two syl-2352 PID's from Auber. I don't have power to my element outlet for my HLT. I have 120v on both leads on the input side of the contactor but only get a little over 1 volt on the output sides. My BK contactor works fine and I have power all the way to the outlet. I also hear a click when I turn on the power to my BK but nothing when I turn on the HLT. I hooked up the switch for my BK to the contactor and still nothing so I know it is not the switch. I checked continuity from my SSR's to the PID's and that is fine so I know it is not a connection there. Any ideas?