garbageman
Well-Known Member
Alright. I'm finishing up my planning and purchasing phase of the the new ebrewery. I have a ebrewingsupply box coming, BCS control and a few other goodies. It will be a RIMS setup using 2 keggles.
My question is I'm adding another circuit to the house box and running to a GFI spa disconnect box. The circuit will be 50a at box with 120v on each leg and neutral. Then 6 ga to the spa disconnect. Out of the spa box will be 4 wire to the control box where it all gets divided up to pumps and elements. Using this guide https://www.homebrewtalk.com/f170/spa-panel-wiring-dummies-266751/
Am I missing anything? Or doing something shady? The only other thing I could think of is 50a GFI breaker at house box and bring 4 wires out and go straight to control panel. Is that safer?
My question is I'm adding another circuit to the house box and running to a GFI spa disconnect box. The circuit will be 50a at box with 120v on each leg and neutral. Then 6 ga to the spa disconnect. Out of the spa box will be 4 wire to the control box where it all gets divided up to pumps and elements. Using this guide https://www.homebrewtalk.com/f170/spa-panel-wiring-dummies-266751/