Wiring 2 temp probes to one PID. Possible?
|
|
I have my wiring figured out with the help of P-J's wiring digrams and many other comments/ideas from the forum. A simple gravity system (i.e. no pumps) with 5500w elements in the HLT and BK. The PID will control the SSR for the HLT, but I would like to also use the same PID/SSR for the BK. I only need to reach 220F (100C) to boil in the BK, but don't want to just turn on the element and boil crazy. Would like to control it to a simple rolling boil and not have the element at full all the time.
Can I put a temp probe in the BK and switch it between the HLT and BK? Woudl a probe be of any help if it is set for 220 deg? Or is there a better way?
(Also thinking of a PWM circuit, but looking for the cheapest/easiest solution. aka, short on $) 
|
|
|
09-15-2011, 01:04 PM
|
#2
|
|
Feedback Score: 0 reviews
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 2,773
Liked 146 Times on 120 Posts Likes Given: 197
|
It is possible to set up 2 probes but that will not help you for what you are trying to do. Once you reach the boiling point the temperature is the same on a gentle boil and a raging boil.
What PID do you have? If it is the Auber Instrument SYL-2352 or SYL-2362, you are in business without any issue. That PID has a manual mode that delivers percent of power to the element. You just need to set up the configuration for manual mode and then you are there with a push of a button.
How can I help you?
P-J
|
|
|
09-15-2011, 04:33 PM
|
#3
|
|
Vendor and Brewer
Feedback Score: 0 reviews
Join Date: Aug 2006
Location: Piscataway, NJ
Posts: 20,769
Liked 478 Times on 340 Posts Likes Given: 9
|
Just to further clarify, you don't even need a probe in the BK in this situation. You can use a single SSR driven off a single PID but the high current side would have to be switched between the HLT and BK via a high current double throw switch or contactor. You could also use two SSRs and use a low current double throw switch to send the PID control signal to the correct SSR (not as safe).
When you switch a PID into manual mode to control duty cycle to the boil kettle element, it doesn't care what the temp probe is sensing.
__________________
BrewHardware.com
Sightglass, Refractometer, Ball Valve, Weldless bulkhead, Thermometer, Decals, Stainless Steel Fittings, Compression Fittings, Camlock Quick Disconnects, Scale, RIMS tube, Plate Chiller, Chugger Pump, Super Clear Silicone Tubing, and more!
|
|
|
09-15-2011, 05:48 PM
|
#4
|
|
Feedback Score: 0 reviews
Join Date: Jan 2011
Location: Saint Augustine, Fl
Posts: 181
Liked 2 Times on 2 Posts
|
Quote:
Originally Posted by Bobby_M
Just to further clarify, you don't even need a probe in the BK in this situation. You can use a single SSR driven off a single PID but the high current side would have to be switched between the HLT and BK via a high current double throw switch or contactor. You could also use two SSRs and use a low current double throw switch to send the PID control signal to the correct SSR (not as safe).
When you switch a PID into manual mode to control duty cycle to the boil kettle element, it doesn't care what the temp probe is sensing.
|
Agreed. There is no reason for multiple temp probes. However, if you want to have multiple temp probes setup to one pid the simplest option may be to purchase multiple probes from auberins and install a temp probe in each kettle, tun, etc. Then just switch the sensor cable connected to the pid (since it has a disconnect) b/w each temp probe.
Hopefully that makes sense. It should be noted, each sensor often has a little bit of variation that needs to be adjusted so your readings may be slightly off.
|
|
|
09-15-2011, 07:03 PM
|
#5
|
|
Mad Scientist
Feedback Score: 2 reviews
Join Date: Nov 2010
Location: , New York
Posts: 4,261
Liked 26 Times on 24 Posts Likes Given: 17
|
I actually just did something similar to this for my build. I used a 3 pole2throw switch and can toggle between two temp probes on the BK and the HLT. Both are on one PID.
As others have mentioned, you can really only have one accurate temp reading unless your temp probes have exactly the same error in reading for calibration (unlikely). So I set the accurate temp probe reading to the HLT and not there is a couple degrees of difference between the real and actual in the BK.
I like to use the temp probe like this for the BK so I can read the temp quickly and estimate when my boil start is getting close, as well as where I am in the chilling process.
This is a little different than your question, but the other guys already aptly answered the PID boil control functionality questions.
As a side note I set my control box up to toggle between the HLT and BK with two contactors as bobby suggested. Based on this I don't have to plug in or unplug anything through the brew session.
|
|
|
09-15-2011, 07:10 PM
|
#6
|
|
← Moster Truck Force →
Feedback Score: 0 reviews
Join Date: Apr 2009
Location: ☼ Clearwater, FL ☼
Posts: 14,168
Liked 1343 Times on 942 Posts Likes Given: 920
|
I have 2 thermocouples and 2 dual SSRs connected to my PID through a 3 pole DT switch. See this post for schematic and other details. I've used it for about 50 batches, so I can confirm it works well
BTW, it is a very good idea to be able to see the temp in your boil kettle if you are chilling in there. I don't understand why this is overlooked so often.
__________________
Mornie utulie,
Believe and you will find your way.
Mornie alantie,
A promise lives within you now....
|
|
|
09-15-2011, 09:59 PM
|
#7
|
|
Feedback Score: 0 reviews
Join Date: May 2011
Location: St. Louis, MO
Posts: 39
Liked 2 Times on 1 Posts
|
Quote:
Originally Posted by P-J
... the Auber Instrument SYL-2352 or SYL-2362, ... has a manual mode that delivers percent of power to the element. You just need to set up the configuration for manual mode and then you are there with a push of a button.
|
Thanks P-J. That's what I didn't know.
Quote:
Originally Posted by CidahMastah
I like to use the temp probe... so I can ... estimate when my boil start is getting close, as well as where I am in the chilling process.
|
Thanks CidaMastah. I hadn't even thought of the chilling process. Now I know I need the probe!
And thanks Bobby M, rsklhm10, and passedpawn. Your comments gave me more useful help for my next steps.
But one more question: I read that a K type probe should not be switched. Do you all agree? Is it better to use an RTD probe if it is to be switched?
|
|
|
09-15-2011, 10:08 PM
|
#8
|
|
Feedback Score: 0 reviews
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 2,773
Liked 146 Times on 120 Posts Likes Given: 197
|
Quote:
Originally Posted by KEG99
...
But one more question: I read that a K type probe should not be switched. Do you all agree? Is it better to use an RTD probe if it is to be switched?
|
You are far better off with the RTD temp probe for many reasons.
|
|
|
09-15-2011, 10:16 PM
|
#9
|
|
← Moster Truck Force →
Feedback Score: 0 reviews
Join Date: Apr 2009
Location: ☼ Clearwater, FL ☼
Posts: 14,168
Liked 1343 Times on 942 Posts Likes Given: 920
|
Quote:
Originally Posted by p-j
you are far better off with the rtd temp probe for many reasons.
|
+1.
__________________
Mornie utulie,
Believe and you will find your way.
Mornie alantie,
A promise lives within you now....
|
|
|
09-16-2011, 12:42 AM
|
#10
|
|
Mad Scientist
Feedback Score: 2 reviews
Join Date: Nov 2010
Location: , New York
Posts: 4,261
Liked 26 Times on 24 Posts Likes Given: 17
|
+1 to PJ's comment - my probes are rtd
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
|
|
|