So my initial question arose when trying to complete the 10 gauge leg feeding the contractor and led 1. Now that I see the led 1 portion can be of smaller gauge, how do you execute this? I'm assuming running 14 gauge back to the terminal bar. Sorry for the noob questions, obviously don't want to use the wrong wire
You can route the finer gauge wire for the switch/LED either to the terminal block, or the power input terminal on the contactor. Or, you can just run a 10 G from the terminal block to the switch/LED, and another 10 G from the switch/LED to the contactor. But the first option is probable easier.
EDIT: There are many branch points shown in nets in the diagram. None of these should actually be wired as splices in the middle of other wires. All wires should terminate at a screw or connector terminal.
And, as Augie noted, you don't even need 14 G for most of the other wiring. All wires carrying the pump current should probably be 14 G, but all of the control circuit wiring could be 18 G.
The way to figure out how much current a wire needs is to trace the current flow to each load device, and then size the wire carrying the load to that device for the required current. In a branched net, not all branches carry the same current, but they do carry the same voltage.
EDIT: Given your apparent unfamiliarity with electrical circuits (as indicated by the level of questions you asked), you should get an electrician, or some other person you trust who has electrical experience, to check your work before powering anything up.