Hi everyone! I finally got my panel wired up and ready to go and ran into this problem right when I started to heat my mash water. Ran an autotun last night and everything worked great. I'm not really sure what's going on?
<iframe width="560" height="315" src="" frameborder="0" allow="accelerometer; autoplay; encrypted-media; gyroscope; picture-in-picture" allowfullscreen></iframe>
 
Last edited:
Looks like bad input from the temp sensor. Do you have a thermocouple or PT100 temp probe? Loose connections anywhere in the temp probe signal path can disrupt temp readings.

Brew on :mug:
 
Looks like bad input from the temp sensor. Do you have a thermocouple or PT100 temp probe? Loose connections anywhere in the temp probe signal path can disrupt temp readings.

Brew on :mug:

I've got a PT100.. Everything seems to be secure with no loose connections.
 
Disconnect the temp probe. Measure between the ends of the same color leads. You should measure ~0 ohms. Then measure between each of the same color leads and the odd colored lead. Both measurements should be ~100 ohms, and exactly equal. If you don't get these readings, then you have a problem with the temp probe.

Brew on :mug:
 
Looks like there might be a loose connection in the probe itself. I've had it happen once, since the probe is sealed I had to throw it away and buy a new one. :(
 