let me start this out by saying I have no electrical experience and after reading the 300 sum od pages of info on this topic im still lost. I am trying to build a temp controller for my garage fridge so I can ferment in it and im not sure on a few things
1. Can I use an extension cord with #16 wires on it or do I need to get another?
2. Can I use the wires from the extension cord to wire up the stc to the outlet?
Any help will be much appreciated.
NOOOO!! AND NOO!!
IMO 16 gauge wire is generally FAR to small to run a refrigerator compressor! 16ga is only good for 12-13 amps. In all seriousness if you run 16ga to a refrigerator that draws over the amperage a 16ga wire can handle you're running a risk of burning your place down!
And I highly recommend AGAINST permanently using extension cords for anything! There is a reason it is against fire code!
For a refrigerator you are going to want a 14ga wire and a 110v 15 amp circuit and the least!
I just built a fermentation chamber and I actually wired a 25 foot plug using 14/2 with a ground using outside wire. The STC-1000 can only handle a 10amp draw on it so a 15 amp circuit would be fine as long as what is drawing on the controller is less than 10amps.
But If your refrigerator draws less than 10 amps then go for it. Otherwise don't let your wiring job become your weakest link!
I really feel you are far better off over sizing the wire and not needing the capacity then trying to skimp on the wire and need the extra capacity.
Sent from my DROID RAZR HD using Home Brew mobile app
By using your reasoning you should not be using a STC-1000 that is rated only for 10A on a 15A circuit. What is your reasoning for saying the you can not use cable with a lower ampacity, but you it is ok to use other electrical componants with lower current ratings. By the way from what I have read the relays are in fact rated for 15A @ 120V.
acafro, forgive me for being thick...i'm not an electrician (nor do i play one on TV), but if the STC-1000 is, in fact, only rated to 10 amps, and a 16GA extension cord to 13 amps, wouldn't the OP be perfectly fine building his controller with wire from a 16GA extension cord??? Cause it seems to me that the STC-1000 would be the weakest link (and fail first, 3 amps worth of draw before his extension-cord-build would give out)...
I am not running a 15 amp system, I am running a 10 amp system on a 15 amp circuit. The circuit is the wiring going from the outlet to the breaker panel and that particular system, is on a 15 amps breaker, thus it is a 15 amp circuit (as is most of the circuits in my house other than 220 volt circuits). Now for the record I am not an electrician and my terminology could be off, but the licensed electrician who helped my with this system seems to feel it is an appropriate set up. The 15 amp circuit merely means that circuit that the fermentation chamber is plugged into can handle up to 15 amps
The system I have set up does not draw more than 10 amps on the controller. So yes, the STC-1000 is appropriate for this particular application.
as far as the STC-100 rating go, here is a picture of the wiring diagram that came with the STC-1000.
10A/220VAC to me indicates the STC-1000 can only handle 10 amps up to 220 Volts AC. Though I could be mistaken...
Firstly sorry, you are right that all the documentation states 10A limit - it is only those that have opened up that have found that the relays are actually also rated for 15A @ 120V.
Your reasoning does not make sense - the cable can handle the expected current, the STC-1000 can handle the expected current. Why would you need to use cable that can handle more current than the breaker can handle for appliance cord. As someone said above if that was the case no appliances would be wired with anything less than 14 AWG.
Why are you distiguishing between two componants both rated below the CB rating and so could potentially (but not likely) be overloaded. You are basically saying that for some reason you trust the STC-1000 to stay together even though the rating says it should, but you don't give the same level of trust to the cable... personally I would trust the cable more
A fair as I am aware most warnigns about contious use of extention cords are due to the fact their is not control over the general publics use of them - i.e. people can easily plug loads over the rated current, if not used continously you would notice your cable is stating to burn/melt/etc. when you put it away.
The system is plugged into a 15 amps circuit, why would I not use 14 GA wire? If you would like to use wire that is smaller than go ahead, I simply do not feel comfortable using wiring that cannot support the total use of the circuit it is plugged into.
I also have other outlets and lights running in the same system that are not connected to the STC-1000, the potential is there to draw up to 15 amps from the system. But the heater and AC I have wired into the STC-1000 draw under 10 amps. I really fail to see why the concept is so difficult to understand nor do I see why it's an issue.
NOOOO!! AND NOO!!
...you're running a risk of burning your place down!
...
Sure. Why not? Now, I'm not sure what your "whole set up" will be but an extension cord can be sacrificed into use as a power cord. And it already has a handy molded plug attached. Individual conductors can be pulled from the sheathing to be used as jumpers if necessary. The entire load of your "whole set up" needs to be considered in sizing the cord.You guys are chopping up extension cords to wire your whole set up?....So I don't need to buy a roll of wire, just hack up a 12ga cord?...
Sure. Why not? Now, I'm not sure what your "whole set up" will be but an extension cord can be sacrificed into use as a power cord. And it already has a handy molded plug attached. Individual conductors can be pulled from the sheathing to be used as jumpers if necessary. The entire load of your "whole set up" needs to be considered in sizing the cord.
I'll toss in a few more cents.
The internal relay of the STC1000 that I own is rated at 15A/125VAC.
[
The paperwork on mine indicated 10A. Unless using a heater above 1000watts or a larger than normal refrigerator or freezer, 10amps is all the device capacity that is needed. Any additional loads, not running through the STC1000, need to be considered only for power cord sizing.Maybe I should look inside mine... the paperwork and stickers say 10 amps. It would be nice to have one rated to 15......
I have a 750 watt space heater that draws 12.5 amps that I would much rather use if my STC-1000 would handle up to 15 Amps...
I have a 750 watt space heater that draws 12.5 amps that I would much rather use if my STC-1000 would handle up to 15 Amps...
Sent from my DROID RAZR HD using Home Brew mobile app
You puzzled me. To draw 12.5 Amp to get 750Watt you should run it at 60Volt. What kind of application do you have?
There is something seriously wrong if a 750 watt space heater is drawing 12.5 amps. Should be about half that at 120 volts.
Watts/volts=amps
On the rating sticker, that appliance are required to have, it reads that the heater draws 12.5 amps. And it is a 750 watt heater I get the mathematics of it. I'm just telling you what the specifications are...
If that's what's on the label, then it can't be a UL approved device. They would never allow that. W/V=A, in this case 750/120=6.25 amps. There'e more to this heater. Are you sure it's not 750/1500 watts? 1500 is 12.5 amps, and this is typical for virtually every space heater made in the last 50 years (I own a heater element mfg business - we deal with these devices all the time).
To those opening your controllers and reading the ratings of the parts - Stop! The ENTIRE device has a rating based on ALL the components in the system. That relay is connected via copper traces on a circuit board, and to the outside via the screw connectors. If it says 10 amps max, there is a reason, very likely the copper traces.
Power cord ratings (actually wire in general) are based on the type of wire, and how it's used. Interior household wiring is 14awg for 15a and 12awg for 20a. This is because the insulation will overheat if you exceed it, and it's rated that way. That same size copper conductor when used inside of a heating appliance is rated higher. If you were to look at the wire inside of that space heater it's very likely smaller gauge, probably 16awg, as it's rated differently, and insulated differently, but still quite capable of handling the current. It will be warm to the touch when at full rating, whereas your typical power cord is (should?) not.
If that's what's on the label, then it can't be a UL approved device. They would never allow that. W/V=A, in this case 750/120=6.25 amps. There'e more to this heater. Are you sure it's not 750/1500 watts? 1500 is 12.5 amps, and this is typical for virtually every space heater made in the last 50 years (I own a heater element mfg business - we deal with these devices all the time).
.
As mentioned above it is alright if the cable gets warm to the touch - depending on its specs the temperature limit of the cable could be between 65°C-90°C. It should not be hot to the touch though!