RMessenger
Well-Known Member
How can I wire this 50 amp spa panel with 12/2 wire (please note that I'm only using it for the GFCI protection and will clearly mark it as a 20 amp line)?
P-J helped me out with this a few days ago. Here's the clicky. Post 8 if the link isn't direct.
https://www.homebrewtalk.com/f170/element-grounding-501908/#post6492464
I'm pretty sure that diagram is wrong. The only place you can connect ground to neutral is in a service entrance panel (usually the main breaker box.) The spa disconnect box is not a service panel.
I'm pretty sure that diagram is wrong. The only place you can connect ground to neutral is in a service entrance panel (usually the main breaker box.) The spa disconnect box is not a service panel.
I've finally had a chance to upload a picture of the instructions for 2 pole that came with the spa panel. They're not as clear as the instructions that I posted at the start of this thread, so I'm a little confused, but doesn't it look as if the instructions say to wire 2 pole the way Watermelon83's link says to?
[QUOTEIn no way, shape, or form is the green from the main service panel connected to a neutral bus.
P-j's diagram is right and safe, if that is what you are referring too. Since you don't have a four wire feed, the grounding in panel discussion is irrelevant to your application.
Just to be clear. You should have two hot wires and the neutral for a 240v element. If your incoming connection color options are red black and white then red and black are your loads white is your neutral.
Going to the panel you NEED those three, not the ground. If I follow you correctly, you want that green wire connected to white not green.