Can a single PID (Auber SYL-2352) control two heating elements in a single kettle?
 
Absolutely. But likely you'll need 2 SSRs wired in parallel each sized for the element it controls
 
...or one single SSR rated to switch the combined power of the two elements ;)
 
To be clear... it can fire as many elements as you want using an array of SSRs slaved to the single SSR output, but it only accepts one temperature probe input.
 
To be clear... it can fire as many elements as you want using an array of SSRs slaved to the single SSR output, but it only accepts one temperature probe input.

To be clearer: it can fire as many SSRs as the PID can source. The 2352 can source up to 30mA which is typically 2 SSRs max.
 
Unless it fires 1 SSR that in turn fires a plethora of other SSR's
 
Unless it fires 1 SSR that in turn fires a plethora of other SSR's

Problematic without the application of additional bleeder resistance. The leakage current of an SSR may also be sufficient to cause the others to turn on randomly.
 
You probably are under 40 amps, so I'd just get 1 40 amp SSR and wire both elements through that. Have a good heatsink on it. If you are using 5500 W elements or something like that you'll need 2 SSRs or a bigger SSR.
 
Problematic without the application of additional bleeder resistance. The leakage current of an SSR may also be sufficient to cause the others to turn on randomly.

Ok, and a resistor between the PID controlled SSR and the other SSR's on the elements. :cross:
 
You probably are under 40 amps, so I'd just get 1 40 amp SSR and wire both elements through that. Have a good heatsink on it. If you are using 5500 W elements or something like that you'll need 2 SSRs or a bigger SSR.

I run a 5500w with 1 SSR. I have a 40amp. I have another SSR for the other element. But, I best keep my mouth shut.:eek:
 
Ok, and a resistor between the PID controlled SSR and the other SSR's on the elements. :cross:

Not quite. :)

Bottom line for the OP is, yes, the PID can easily drive two SSRs. I've not seen a brewing setup where more than two needed to be driven simultaneously, but if the situation arose, there are much better, more cost-effective ways to do so than cascading SSRs.
 