Ok, your terminology was a bit odd. When you said splice, I thought you meant connect together. Sorry for the misunderstanding.
With a load having a significant impedance (AC resistance), connecting L1 on one side and L2 on the other is not a short. A short is equivalent to a ~0 ohm load. A 5500W 240V element has reisistance of about 10.5 ohms, so will draw about 240V / 10.5 ohms = 22.9 A. The contactor coil has an AC impedance more like 9600 ohms, so will draw something like 240V / 9600 ohms = 0.025 A or 6 W power. Note that the DC resistance of the coil is lower than the AC impedance, and will be about 1800 ohms (if you measure it with a meter.)
Brew on
With a load having a significant impedance (AC resistance), connecting L1 on one side and L2 on the other is not a short. A short is equivalent to a ~0 ohm load. A 5500W 240V element has reisistance of about 10.5 ohms, so will draw about 240V / 10.5 ohms = 22.9 A. The contactor coil has an AC impedance more like 9600 ohms, so will draw something like 240V / 9600 ohms = 0.025 A or 6 W power. Note that the DC resistance of the coil is lower than the AC impedance, and will be about 1800 ohms (if you measure it with a meter.)