NattyBrew
Well-Known Member
No where close to an expert, but I think fill does not apply since you are using conduit for protection. Did you fish the wire through or push it? How many 90's you have. Again no expert.
Mild you absolutely beat me to the punch! I have been WAY over researching this thing and found that like most codes, there is a ton to learn. To the best of my research, my system is technically a "sleeve" for protection of the NM-B cable, and not a conduit system since it does not run completely between one electrical box to another. There is nothing I can find in my 2008 NEC handbook that prohibits Romex from being run in conduit, and I can only find confirmation that Romex should be protected with a sleeve of conduit in exposed locations where the wire could be damaged via 334.15.
I also found verification that conduit fill rules do not apply to my setup in Chapter 9, Table 1, Note 2 that:
Table 1 applies only to complete conduit or tubing systems and is not intended to apply to sections of conduit or tubing used to protect exposed wiring from physical damage.
So as far as my reading of the NEC, my protective sleeve is not required to meet NEC fill rules, even though by my calculations above it does and just barely! I have been wrong before, and I still may be here, but I think with the amount of research and reading I've done with my copy of the NEC I am confident my setup is very safe and 99% within code.
I think I will stop beating Barbaro here (too soon?) and move on to more of my build!