Junkster said:If you temperature sensor is a thermocouple, try reversing the leads; also, make sure any configuration parameters in the controller set-up are correct.
SSR's leak a little - try putting a 100w light between the load side & common and see how it responds by looking at its relative brightness.
Thanks Junkster, you're two for two.
Swapped the + and - on the thermocouple leads and now it works. Funny since the leads were marked ... incorrectly!
Also, with a 75w lamp wired in, the SSR is switching correctly.
I'm reading about SSR reset failure and yes, it seems most SSR do leak on the load side, and a load must be greater than the leak in order to reset.
So, question is, is the leak enough to get you in trouble in any situation where you expected the circuit to be cold? Good thing I wired a contactor load side or the SSR.
Thanks,
Kevin