While its fine to over build it for this application, Ive been told numerous times that the continuous load rule only applies to circumstances where full continuous load will be applied to the circuit for more than 3 consecutive hours. I dont think anyone will be powering a 5500w element in a home brewery at 100% power for 3 hours. Not for home brewing beer anyways..
To quote clifford power
http://www.cliffordpower.com/stuff/...496ba/misc/is_37_80_versus_100_rated_ats1.pdf
"5.0 Continuous Loads:
In Article 100, NEC defines a continuous load as “a load where the maximum current is expected to
continue for 3 hours or more. It is therefore critical to understand that this is a load at its maximum current, uninterrupted for at least 3 hours. Office lighting typically meets this qualification.
OCPD size = 100% of non-continuous load + 125% of continuous load. Sec. 384-16 (c) has the same requirement
except that it is stated in terms of loading of the OCPD. This rule states that an OCPD can be loaded to only
80% of its rating for continuous loads. We should remember that 80% is the inverse of 125% (0.80 = 1 divided
by 1.25) and as such, the rules are indeed identical in their end requirement.
Note!
Read the rule carefully - the 125% sizing of the OCPD (or 80% loading) is ONLY applicable when
continuous loads
are involved. CBs and other OCPDs can be sized at 100% of their rating for any NON-
CONTINUOUS load applications."
A 25a rated circuit will work fine for an element that peaks at 23a and will generally be used in a non continuous pwm or pid controlled application. its worked well for me for years. Ive never had a fuse pop or breaker trip and my wiring does not get hot.
Out of the 5 elements I have only 2 draw 23 amps most end up being a few hundred watts less than the rated size. my HLT element for example is supposed to be 4500w but is actually 4040w peak and draws less than 17 amps peak if I remember right..