Well-Known Member
Hi All -
Need some advice. Last week I ran the inaugural brew on my updated system (half barrel). I have a 50 amp box providing power to HLT (5500 watt element), Boil Kettle (5500 watt element), and RIMS (4500 watt element). Obviously I can only run 2/3 elements at one time.
The issue was my HLT element - it was only pulling 8-9 amps. Heated fine, but certainly not hitting the full 5500 watts. The boil kettle was pulling closer to 20 amps. I checked voltage and it was right on at 240v. Resistance came in at about 10.5 ohms (which seems ok?).
I suspect it may be an issue with the element itself. I have since replaced it with a new element but have not tested it.
Thoughts? Could there be another reason why the element was not pulling the full amperage?