Hi there,
This is not a keezer (at least for now), but I think this forum is the best source of information for these conversions.
I converted a deep freezer into fridge with the STC-1000+, and test ran it yesterday. I inserted my temp probe into the original place after I pulled the original probe out. My intention is to run it around 32 F and store large quantities of meat in there. And when I don't need it for that, it's time for some brewing ;-)
It runs fine, but it runs pretty frequent and I have a hard time keeping it stable. It is pretty empty, but I tried to add some thermal mass with 3 x gallon bottles of cold water in there.
My set point is 32 F, but after the compressor stops it gets a lot colder, down to 25 F. And vice versa, it gets a lot warmer than my set point + hysteresis is set to. In other words, there is pretty long delay for the cooling to start/stop after the compressor kicks in/out. My cooling delay is set to 5 minutes currently and the compressor almost cycles that frequently.
Would placing the temp probe into small glass of water help? I wouldn't want it to run too cold for too long, so the meat doesn't start to freeze on the outside. Generally meat starts to freeze around 29 F.
Is it a good practice to try to emulate "meat temperature" by the water, or just try to stabilise the air temperature around 32 F? I shouldn't have the need to add anything warm in there, just meat that has been transported in ice to my place.
I was thinking of raising my set point to around 35 F and setting my hysteresis to zero to try to counter the extended cooling after getting down to the set point...
Or should I just fill it with thermal mass and give it few days to stabilise?
This is not a keezer (at least for now), but I think this forum is the best source of information for these conversions.
I converted a deep freezer into fridge with the STC-1000+, and test ran it yesterday. I inserted my temp probe into the original place after I pulled the original probe out. My intention is to run it around 32 F and store large quantities of meat in there. And when I don't need it for that, it's time for some brewing ;-)
It runs fine, but it runs pretty frequent and I have a hard time keeping it stable. It is pretty empty, but I tried to add some thermal mass with 3 x gallon bottles of cold water in there.
My set point is 32 F, but after the compressor stops it gets a lot colder, down to 25 F. And vice versa, it gets a lot warmer than my set point + hysteresis is set to. In other words, there is pretty long delay for the cooling to start/stop after the compressor kicks in/out. My cooling delay is set to 5 minutes currently and the compressor almost cycles that frequently.
Would placing the temp probe into small glass of water help? I wouldn't want it to run too cold for too long, so the meat doesn't start to freeze on the outside. Generally meat starts to freeze around 29 F.
Is it a good practice to try to emulate "meat temperature" by the water, or just try to stabilise the air temperature around 32 F? I shouldn't have the need to add anything warm in there, just meat that has been transported in ice to my place.
I was thinking of raising my set point to around 35 F and setting my hysteresis to zero to try to counter the extended cooling after getting down to the set point...
Or should I just fill it with thermal mass and give it few days to stabilise?