After a second reading.....
You want to put a NORMAL 60A breaker in the main panel and feed the subpanel with it, and then use two 30A GFCI breakers in the subpanel to power your brewery.
That should work fine.
Yes I should have been more clear - a regular 2pole 60 amp breaker (not the junk GFI one I bought).
Out of curiosity, could the 60 amp gfi one I bought work? I hadn't even thought of using that from the load center. But if there are 2 30 amp GFI breakers in the subpanel they will be adding the neutral from the subpanel.
I assumed that with the 60amp GFI breaker's intended wiring (one neutral) it may render it no usable