GFCI breaker neutral is bonded with ground in main panel bus bar
Did you ever check the gfci breaker wires to see if they are set up properly. The most common cause of a 240v gfci breaker tripping as soon as power is applied through it is the load nuetral is bonded to the buss bar. It NEEDS to be on the load nuetral of the breaker itself. Very common issue. The permanent white wire coming out of the breaker goes to nuetral buss bar. Nuetral wire from your controller outlet goes to load nuetral on the breaker.
Ha ha, cause no one has wire running through wood in thier house right?
Thats not what I asked... Where is the white wire landed that goes to your outlet for the panel? Is it on the bus bar or is it on the breaker?
Thats what I was getting to. You might want to look into getting a refund from the electrician you hired.
Those cables are approved for that use, using wood as an enclosure is almost the dumbest thing I've seen in a while, the dumbest is your comment.
That is your opinion. Been making enclosures out of wood for 15 years. Never had a fire yet. If you dont like my methods fine, didnt ask for your approval.
Yeah. It looks like you got boned by your electrician. There should be two white wires connected to your GFCI.
Maybe there's something I'm missing or it's not shown in the photo of your panel, but is there a grounding electrode conductor in the panel? There should be a larger ground wire from panel ground to earth ground.
The three coming in from utility are hot, hot and neutral.This is the main panel, I don't think I'm seeing the grounding electrode unless it is one of the 3 main black wires coming in...?
The three coming in from utility are hot, hot and neutral.
I'd get an electrician, not the one who installed your GFCI, come and take a look and properly ground your system.
This would be good to know, I made an assumption that this panel is feed directly from utility, which it may not be.Are you in an apartment or multi dwelling house?
This would be good to know, I made an assumption that this panel is feed directly from utility, which it may not be.
Good to know. I thought it would be, but wasn't 100% sure without the code book in front of me.Yea but a ground is still required. Just may be easier to run if there is an existing code compliant ground system in place.
Are you in an apartment or multi dwelling house?
I agree, before you start putting electricity in water, get a proper ground. Even though a GFCI doesn't need a ground.
I'm in a single family house... so, there is no ground rod installed?
I found this article for the OP. It is great at explaining what Trimixdiver1 is trying to convey. To the OP, this would only take about 5 min to read and it will be worth your time to help understand what is really going on with an electrical system and the importance of grounding.
http://www.ashireporter.org/HomeIns...d-Grounding-and-Bonding/1906#WordE3501-02.jpg
About 2/3 of the way down it talks about A homes grounding system specifically. So this is what you are looking for, or when you hire an electrician this is what they should be doing for you.
I found this article for the OP. It is great at explaining what Trimixdiver1 is trying to convey. To the OP, this would only take about 5 min to read and it will be worth your time to help understand what is really going on with an electrical system and the importance of grounding.
http://www.ashireporter.org/HomeInspection/Articles/The-Word-Grounding-and-Bonding/1906#WordE3501-02.jpg
About 2/3 of the way down it talks about A homes grounding system specifically. So this is what you are looking for, or when you hire an electrician this is what they should be doing for you.
Right on. Actually I think this would be very relevant for many to read because many have an improper concept of what "ground" actually is. Understanding the difference between 'grounding' and 'grounded' is not complex, but that understanding can help tremendously if one were messing around with electricity.
What I don't know is when the grounding electrode became required for buildings. So I believe many older homes do not have this safety feature. Likewise the simple concept of having a grounding conductor in homes didn't become standard practice until the late 1960s. So if you live in a home built prior to 1968 (I believe) you may still have a non-grounding electrical system. Or the difference between having a two prong plug and a three prong plug.
Rather than scare Bwerner into thinking that something is terribly wrong with his homes electrical I would say that his home was most likely built to the standard of its time, but those standards may not meet the latest and greatest.
So without becoming to long winded, with regard to the original question it looks like your GFCI breaker is your problem looking through the last few posts. Once you get that resolved your panel will 'most likely' work.
BTW your wiring looks much better IMO. I can't tell if everything is totally correct but it looks good without my getting in depth with tracing every wire. With this being your first panel build there is a very steep learning curve to conquer. Hopefully you have learned a lot along the way so if you should endeavor to build something similar in the future you know some pitfalls to watch out for before you start.
Once again, good luck.
[edit]
Found it for anyone interested. A short list of when some electrical items become required for buildings. Way earlier than I expected actually. Looks like 1913 was when it became required that electrical systems have grounding. This is counter to what I wrote above but I left that in tact just because.
Here is the link https://www.dli.mn.gov/ccld/PDF/eli_GFCI_history.pdf
Also for recepticals the date was 1962 (Instead of 1968) where plugs became required to have a ground conductor.
ahem..... shot down in flames for being an id10t for a wooden enclosure...... ERRM, YESBack then things were bonded and not grounded. There is a difference.
I would venture a guess that what is coming to the neutral bar is the ground. It is that way with mine. The power company provides me with two hots and no neutral. I have to provide a ground which doubles as my neutral. I believe they call floating neutral.