OK,

So I'm finally getting ready to build my walk in la John Beere with the air conditioning unit to cool it.

I have a question, though. Since I live in Iowa, it gets below freezing in the winter. Has anyone used a standard window air conditioner in a cold weather area? I'm worried that the coils will freeze in the winter, and will ruin the a/c unit.

I'm also considering one of the stand-alone a/c units that only need to vent out, but those are about 3X the price.

Thanks for the help,

drost
__________________
"It isn't a matter of being a beer snob. Some people think a steak from Ponderosa is a great dinner out (Budweiser). Others would rather have a filet at one of the better steakhouses (craft beer). " --Pronger750


 
Reply With Quote
Old 07-31-2008, 09:03 PM   #2
drost
Recipes 
 
Apr 2006
Ankeny, IA
Posts: 171

no one, huh? That's what I was afraid of....
__________________
"It isn't a matter of being a beer snob. Some people think a steak from Ponderosa is a great dinner out (Budweiser). Others would rather have a filet at one of the better steakhouses (craft beer). " --Pronger750

 
Reply With Quote
Old 07-31-2008, 09:11 PM   #3
Loup
Recipes 
 
Jul 2008
Minnesota, Twin Cities area
Posts: 273
Liked 3 Times on 2 Posts


I had a window AC unit at my apartment, it was left in place all winter, I never tried actually running it in the winter, but it was perfectly happy to just sit there. You could try installing some sort of vent that simply let in cold, outside air during the winter that had a servo that would open and close it when needed.

*edit* I live in Minnesota

 
Reply With Quote
Old 07-31-2008, 10:15 PM   #4
pen25
Recipes 
 
Jun 2008
tulsa, ok
Posts: 976
Liked 2 Times on 2 Posts


you can get a cover for the ac unit, but its only to keep the cold air out. it wont damage the ac unit but its good to cover it as it keeps junk out of the unit.

 
Reply With Quote
Old 07-31-2008, 11:06 PM   #5
John Beere
Deep Six Brewing Co.
HBT_LIFETIMESUPPORTER.png
 
John Beere's Avatar
Recipes 
 
May 2006
Valdosta, GA
Posts: 2,051
Liked 59 Times on 40 Posts


I got nothing...

 
Reply With Quote
Old 07-31-2008, 11:12 PM   #6
jcarson83
 
jcarson83's Avatar
Recipes 
 
Jun 2006
Springfield, MO
Posts: 928
Liked 16 Times on 11 Posts


It won't hurt it. They're made to be left outside year round. You could even use it to circulate air when its not hot enough to run the cooling part of it.

 
Reply With Quote
Old 08-01-2008, 04:34 AM   #7
kladue
Senior Member
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Dec 2006
Turner, Oregon, Oregon most of the time now
Posts: 2,305
Liked 53 Times on 47 Posts


Here are a couple things to consider, with high summer humidity any air transfer into the cooler adds to the cooling load by the increased moisture you will condense on the coils. Water vapor travels from the warm area to the cold area so vapor barrier goes on the outside of the cooler structure to prevent moisture buildup and rot in the framing. The lower the air infiltration into the cooler the happier the cooling unit will be. Air conditioners use a flow restriction tube to meter refrigerant with condensor running 80+ degrees F, when condensor temp falls the inside coil temp goes way below freezing as there is not enough refrigerant flow and compressor heats up from lack of refrigerant flow to cool motor. On commercial units the condensor fan is cycled to maintain high side pressure on cold days, you might be able to partially cover outdoor coil to get enough heat buildup to make AC unit work in winter.

 
Reply With Quote
Old 08-01-2008, 02:37 PM   #8
david_42
 
david_42's Avatar
Recipes 
 
Oct 2005
Oak Grove, Oregon, USA
Posts: 25,597
Liked 155 Times on 145 Posts


Many A/C units have a vent position. If you are using an external temperature controller, you could use that position in the winter.

As far as the A/C unit itself & freezing weather, they can handle it.
__________________
Remember one unassailable statistic, as explained by the late, great George Carlin: "Just think of how stupid the average person is, and then realize half of them are even stupider!"

"I would like to die on Mars, just not on impact." Elon Musk

 
Reply With Quote
Old 08-01-2008, 04:49 PM   #9
Chriso
Broken Robot Brewing Co.
HBT_LIFETIMESUPPORTER.png
 
Chriso's Avatar
Recipes 
 
Oct 2007
Someplace, Nebraska
Posts: 4,681
Liked 76 Times on 66 Posts


Is the room below-ground? In that case, cooling it should be a moot point.

However, I'd invest in a dual-stage temp controller so you can run a space heater when the temps get too low.
__________________
BROKEN ROBOT BREWING CO.

Chriso || BJCP Certified || SMaSH Brewers, Unite! || Nebraska Brewers! || Lincoln Lagers Brew Club
"You have just experienced the paradigm shift that is....all grain brewing." - BierMuncher

 
Reply With Quote
Old 08-01-2008, 06:11 PM   #10
jspence1
 
jspence1's Avatar
Recipes 
 
Jul 2008
Hamilton, Ontario
Posts: 1,039
Liked 10 Times on 10 Posts


Definitely don't want to run it in the winter. But you can keep it in place all winter it won't hurt it.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building a walk in. Bsquared Fermenters 26 11-18-2009 08:09 PM
want a walk-in in the PNW ChshreCat Fermenters 0 08-16-2009 02:31 AM
Walk in cooler jacobdaughtry Equipment/Sanitation 2 09-27-2008 05:13 AM
Walk THIS way... alemonkey General Chit Chat 1 09-11-2006 04:36 AM
Another cake walk david_42 General Techniques 2 07-12-2006 06:46 AM


Forum Jump