I have two choices: an easy 3-wire or a difficult 4-wire, cost would be about the same.
1) I have a 3 prong dryer outlet 15 feet from my brew station. I can use a spa panel to convert to 4 lead. Quick, easy, and 30A will cover my needs.
2) I used to have a spa, and one of the artifacts of that spa is an 40 foot run of 4 lead cable with a non-GFI 50A breaker. I can salvage that cable and re-run it to my desired brewing location (a big job), then wire into a spa panel.
Two disadvantages to option #2: relocating the cable will take half a day, and I might want to install a spa again someday.
The question:
Since the 3-wire dryer source will still use a shared ground/neutral, does the spa/GFI essentially provide the same safety as a 4 lead GFI set up?
I’m willing to tolerate the two disadvantages of option #2 as long as there is notable additional safety by using the 4 lead over the 3 lead.
Thanks a bunch…
1) I have a 3 prong dryer outlet 15 feet from my brew station. I can use a spa panel to convert to 4 lead. Quick, easy, and 30A will cover my needs.
2) I used to have a spa, and one of the artifacts of that spa is an 40 foot run of 4 lead cable with a non-GFI 50A breaker. I can salvage that cable and re-run it to my desired brewing location (a big job), then wire into a spa panel.
Two disadvantages to option #2: relocating the cable will take half a day, and I might want to install a spa again someday.
The question:
Since the 3-wire dryer source will still use a shared ground/neutral, does the spa/GFI essentially provide the same safety as a 4 lead GFI set up?
I’m willing to tolerate the two disadvantages of option #2 as long as there is notable additional safety by using the 4 lead over the 3 lead.
Thanks a bunch…