BCS Panel Wiring..so little idea what Im doing

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

SurferMatt

Member
Joined
Sep 17, 2009
Messages
18
Reaction score
0
Location
NJ
What I'm currently trying to do is control fermentation temps on six individual tanks. To do that I have immersion chillers in each tank. Chilled glycol will be supplied by a constantly running glycol pump with a leader line. Each tank gets supplied from a solenoid valve opened by the BCS 462 controller. I recently scored six ssr's off ebay but am not sure of how to properly wire this unit or even power it. I'm very new to this stuff and have explored the site quite a bit but I could really use some help. Can somebody please share some information on wiring ssr's/solenoid valves/BCS/power supplies?
Thanks for all the help.
 
What is the power requirement for the solenoid valves?

Basically the SSR acts as a switch. The BCS puts out 5 volts or so, so if your solenoid requires more than that you can use the SSR's you bought. Hopefully you got the correct ones to control the power needed. Hard to give you precise wiring until we know what you have exactly. The BCS website forum has some diagrams and info from people who have wired BCS set ups.

The BCS comes with a wall wort transformer, plug it in and it should power up.
 
I'm doing this from my head so it could easily be wrong but it should get you close.

Step 1: install 6 temp probes and wire them to the BCS. The probes are two wire, one goes to it corresponding number and the other wire goes to ground on the BCS.

Step 2: (assuming solenoids are 110v 2-wire leads) wire the hot leads from the solenoids to #2 on each SSR or the upper right side.

Step 3: run your 110v power to terminal #1 or upper left terminal. You will most likely need a distribution block or something to feed 6 solenoids from a single power source.

Step 4: Wire the other wire ( neutral) of all solenoids together with your MAIN nuetral.

Check by BCS in manual mode, set all 6 outputs to cool mode and to PID. Set the temp to something like 90* or anything above ambient temp. and the valves should open.

My advice, try it with one fermenter and repeat it once you get it.
 