I just put my control panel together and bought the switches. They are 125v @ 10a rocker switches. I am running a 120v system so i'm fine there. However on two of the connections I will have a 2000w element hooked to it. That will pull 16.5a. Will these switches be ok or do I need larger ones? I see the automation direct ones are only 6a. Now with the one heatstick I can use the signal line to shut it off. That is for the HLT. The second will be turned on for the boil. This will be a straight, on/off connection. Let me know what you guys think.
Thanks,
Brent
**this is running off of two 20a circuits.