So I have a dilemma The short version is: how do I know if it is the PID or the RTD probe that is messed up?
So . I have a direct from China RTD probe that looks pretty nice. It is this one here: http://www.amazon.com/gp/product/B00FHVBKC4/?tag=skimlinks_replacement-20. It looks like a solid no-nonsense piece of equipment. It does not appear to be flawed or leaking, and electrical tests seem to work at room temp.
And I have this PID (a Fuji PYZ-5) which was a donation. Aside from it being old, I was told nothing about how it works. Here is the manual http://home.hit.no/~finnh/lab_fuji_controller/TN2PYZDe-E.pdf. It is an OLD PID. I know that.
Here is where it went wrong: I put the temp probe in a tee after my pump and plugged it into the PID. At this point, the whole system exists to ONLY read the temp of the fluid flowing in the tee past the pump. The PID reads a normal temp at room temp and, as I add heat and circulate water, the PID indicates that temperature is increasing. Then, at a random point after 125 deg F, the PID reverts to showing UUUU in the display indicating one of the following conditions (from page 6 of the manual linked above)
Burnout of resistance bulb sensor (upscale burnout) -① In case of upscale burnout (standard) OFF or less than 4 mA in reverse action ON or more than 20 mA in normal action.
Or
PV reading is more than "the range upscale value +30% FS" NOTE: Even when the PV value is over the range within +30% FS, it becomes sensor burnout display, and the control output is output, if the input voltage exceeds the burnout detecting point.
I have run tests and found that the error occurs at seemingly random temps. Once at 125, once at 167, another time at 150F. I am going to try some more with boiling water tonight but I want to know what I can do to see if it is the PID or the RTD that is causing this trouble? Any ideas or thoughts on tests to run?
I dont mind buying a new PID or RTD if that is the problem but I dont want to buy a PID and a new RTD if only one of them is causing the trouble. Thanks in advance! N_G
So . I have a direct from China RTD probe that looks pretty nice. It is this one here: http://www.amazon.com/gp/product/B00FHVBKC4/?tag=skimlinks_replacement-20. It looks like a solid no-nonsense piece of equipment. It does not appear to be flawed or leaking, and electrical tests seem to work at room temp.
And I have this PID (a Fuji PYZ-5) which was a donation. Aside from it being old, I was told nothing about how it works. Here is the manual http://home.hit.no/~finnh/lab_fuji_controller/TN2PYZDe-E.pdf. It is an OLD PID. I know that.
Here is where it went wrong: I put the temp probe in a tee after my pump and plugged it into the PID. At this point, the whole system exists to ONLY read the temp of the fluid flowing in the tee past the pump. The PID reads a normal temp at room temp and, as I add heat and circulate water, the PID indicates that temperature is increasing. Then, at a random point after 125 deg F, the PID reverts to showing UUUU in the display indicating one of the following conditions (from page 6 of the manual linked above)
Burnout of resistance bulb sensor (upscale burnout) -① In case of upscale burnout (standard) OFF or less than 4 mA in reverse action ON or more than 20 mA in normal action.
Or
PV reading is more than "the range upscale value +30% FS" NOTE: Even when the PV value is over the range within +30% FS, it becomes sensor burnout display, and the control output is output, if the input voltage exceeds the burnout detecting point.
I have run tests and found that the error occurs at seemingly random temps. Once at 125, once at 167, another time at 150F. I am going to try some more with boiling water tonight but I want to know what I can do to see if it is the PID or the RTD that is causing this trouble? Any ideas or thoughts on tests to run?
I dont mind buying a new PID or RTD if that is the problem but I dont want to buy a PID and a new RTD if only one of them is causing the trouble. Thanks in advance! N_G