I'm sorry if some one has posted this before, but is there a heating chart for kw to gal with temp and time? I searched but could only find formulas that had 2/3 of the answer.
There are problems with the spreadsheet.
For example:
The maxumim load for a 15 Amp breaker & #14 AWG house wire is 15 Amps, not 12 Amps.
The maximum load for SJOOW #14, 300V, 3 wire extension cord is 18 Amps, not 12 Amps.
And this statement is incorrect:
"Always use an extension cord the same size as the wire on the Sizing chart or heaver. A smaller extension cord will cause a voltage drop and may cause a fire. If the cord gets warm it's too small and don't use it!"
The sheet is using the 80% rule, another highly debated topic.
The 80% rule is accurate - it's what derates #14 house wiring DOWN TO 15 amps. Applying the rule to derate the current again after it's been applied once does not make since to me.
You'll have to excuse me as I mostly deal with the CEC but....
In the case of 14AWG wire, the NEC mandates a maximum 15A over current device. The over current devices we use (on a residential scale) are all only rated for 80% continuous load. If the load is continuous (which I usually argue in our case it is not) then the 80% applies to the over current device rating (aka 15A->12A in this case).
The spreadsheet is not going to cover all cases in details, and is not meant to replace the advice of a professional. ...
So for a 15A rated breaker, you cannot have more then 12A of continuous load. Your average residential breaker does not have the 100% rating according to the NEC.(A) Continuous and Noncontinuous Loads. Where a
branch circuit supplies continuous loads or any combination
of continuous and noncontinuous loads, the rating
of the overcurrent device shall not be less than the noncontinuous
load plus 125 percent of the continuous load.
Exception: Where the assembly, including the overcurrent
devices protecting the branch circuit(s), is listed for operation
at 100 percent of its rating, the ampere rating of the
overcurrent device shall be permitted to be not less than the
sum of the continuous load plus the noncontinuous load.