The neutral wire on a NEMA 10-30 or 10-50 (10-50 is used for an electric range) is not a normal neutral. It has to originate in the service entrance panel, not a subpanel. So it makes a perfectly good and acceptable ground. The neutral wire from a subpanel is not safe to use as a ground. (unless it's a subpanel in an outbuilding that bonds the neutral again) Grainfather not knowing if a NEMA 10 is wired correctly is a little different than knowing if a NEMA 5 or 6 is correct; those can originate from a subpanel with no problems.